hi folks, got a CU change to do. flat rewired circa '70's. wylex 3036 fuses.
my concern is earthing conductors. at present they are 6.0mm. TN-S.
Pefc is 700A. not sure of main fuse size, so have taken worst scenario at 100A.
referring to tables, @ 700A the disconnect time for a 100A BS1361 is 2 secs. so the adiabatic gives a S of 6.91 for the MEC.
thoughts. please.