Currently reading:
Can a fuseboard be mounted sideways (not me)

Discuss Can a fuseboard be mounted sideways (not me) in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
7
I’m following an electrician and he has fitted a couple of boards sideways
And has said he spoke to manufacturers and they said it’s ok(that old chestnut)
It’s something I’ve never seen and I started when wham were in the charts.I’m testing them need people’s opinion plz
 
My only concern would be the door covering the MCB's, isnt that metal to contain any fire, they normally open up so when you let go they naturally fall to cover the MCB's. Fitting sideways could compromise this, probably ok with some where they have a latch, just fit a sign that says keep closed when not in use or something.
That's a good point!
 
MCB's are vented top and bottom for natural draught cooling of the internal thermal element. Mounting them sideways will reduce the airflow and hence raise the internal temperature. Might not be an issue in the UK but in higher ambient temperature areas it could affect the thermal tripping curve. When we install MCB's in hot climates like tropical and deserts we apply a derating factor to the current rating that's stated on them to aviod nuisance tripping issues.
 
MCB's are vented top and bottom for natural draught cooling of the internal thermal element. Mounting them sideways will reduce the airflow and hence raise the internal temperature. Might not be an issue in the UK but in higher ambient temperature areas it could affect the thermal tripping curve. When we install MCB's in hot climates like tropical and deserts we apply a derating factor to the current rating that's stated on them to aviod nuisance tripping issues.
fair comment, but does not explain why the MCBs are OK mounted horizontally in a TPN board.
 
I'm not sure either Tel, I can only guess they're built to mitigate the warmer operating temperatures.

If we build a panel for warm climate location we sometimes leave a vacant space between each of the MCB's for better ventilation to avoid nuisance tripping.

The ABB catalogue states
1) The thermal releases are calibrated to a nominal reference ambient temperature; for B and C the reference value is 30 °C.
In the case of higher ambient temperatures, the current values fall by approx. 6 % for each 10 K temperature rise.
 
Last edited:

Reply to Can a fuseboard be mounted sideways (not me) in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock