Search the forum,

Discuss Can you sign off any work with a 30ma RCD. in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
2
Hi, my question is. If I have an old wylex consumer unit with NB type 2 breakers (not 60898). Or let's say any CU for that matter. If it's protected by a 30ma RCD, will that pass the cert?. Or for example will the use of old mcbs not be up to standard. Thanks
 
The installation needs to be in a safe condition to extend.
Any new circuits or alterations need to meet latest regulations.
It's theoretically possible to comply using a rewireable board.

Numerous questions come to mind, for for starters:
Where is the RCD installed, between meter tails and consumer unit, or at the start of the new circuit?
Has a surge protection device been installed?
Is the lighting in the extension RCD protected?
Is there a bath or shower room in the new extension?
 
No, new ring has been wired to a new extension at the back of the house and just needs an EIC.

The installation needs to be in a safe condition to extend.
Any new circuits or alterations need to meet latest regulations.
It's theoretically possible to comply using a rewireable board.

Numerous questions come to mind, for for starters:
Where is the RCD installed, between meter tails and consumer unit, or at the start of the new circuit?
Has a surge protection device been installed?
Is the lighting in the extension RCD protected?
Is there a bath or shower room in the new extension?
 
Thanks for the reply This is the puppy, RCD protecting all circuits in the house. Everything past this consumer unit meets regs. If RCD is testing fine and all other tests are fine. Would this be acceptable to sign off, or would most go down the consumer unit change route?
 

Attachments

  • Screenshot_2022-07-23-21-54-40-74_99c04817c0de5652397fc8b56c3b3817.jpg
    86 KB · Views: 30
In general I can't see why under amendment 1 this couldn't be extended. There's a reg recommending dividing the installation to avoid nuisance tripping.
Pragmatically, the RCD is very old and I wouldn't trust it too much. Is this a TT installation?
There's a few reasons I'd rather not, but I don't think I'd be prevented from doing so.

From September (Amendment 2) there would need to be a statement saying no SPD is required, and I'd not be adding a sockets circuit protected by a type AC RCD.
 
In general I can't see why under amendment 1 this couldn't be extended. There's a reg recommending dividing the installation to avoid nuisance tripping.
Pragmatically, the RCD is very old and I wouldn't trust it too much. Is this a TT installation?
There's a few reasons I'd rather not, but I don't think I'd be prevented from doing so.

From September (Amendment 2) there would need to be a statement saying no SPD is required, and I'd not be adding a sockets circuit protected by a type AC RCD.
Thanks for the info. It's a tncs
 
Ok, so it's a PME supply.

Are the meter tails 25mm and is the earthing conductor 16mm?
Bonding conductors 10mm?

Plastic CU is not an issue unless thermal damage is noticed.

There's also the question of maximum demand of 63A at the RCD being exceeded here.

Lighting - 66% of total current demand for each circuit
Power - 100% of the first ring circuit + 40% of all other circuits
Cooker - 10A + 30% of remaining rated current + 5% if the CCU has a socket outlet
Shower - No diversity allowable
Instantaneous water heater - 100% of largest heater + 100% of second largest + 25% of of any others
Thermostatically controlled water heater - No diversity allowable
Underfloor heating - No diversity allowable

Does the test button on the RCD function ok?
Does the RCD trip within 40ms on a 5x test?
Does the EFLI of each circuit measure below the max zs?
Clearly IR is good on each circuit as you would have nuisance tripping otherwise.

At the end of the day, it is irrelevant what the customer wants. You are the qualified & competent person carrying out the inspection and it's your professional opinion that matters here.

Ultimately, is the electrical installation safe for continued use?

You can run yourself in circles questioning yourself with EICR's.
Take a step back, look at the installation as whole and make a professional judgement based on what you see.
 
There's the non-combustible consumer unit question too.
You don't have to change a plastic CU to install a new circuit, though.

It's not ideal but I feel that if the new installation meets regulation standards it would be OK...as long as the existing installation supply requirements are also up to standard.
Plenty of questions need answering, as you say.
 
Last edited:
You would have to note the rcd as a departure from current Regulations. Although it is probably as reliant as a current device BS4293 is no longer recognised under BS7671 for providing additional protection. The same applies to the 3871 mcbs.
 
being pedantic an EIC or EICR is not a pass or a a fail. any deviation from regs should ne noted on the cert. and (with an EICR) coded accordingly. as for the single RCD for alll circuits is concerned, this would be a C3 coding (division of circuits so as to minimise danger and/or inconvenience in the case of a RCD trip).
 
No, new ring has been wired to a new extension at the back of the house and just needs an EIC.

The time for deciding if the existing installation is compliant and safe for continued use would have been before any new work has been completed or even quoted for.

It shouldn't be that an additon has been made and then at the point of testing the customer is informed that they now have to pay more for upgrading to be compliant than they have just spent on new works.
They may now not have the money but if forewarned could have budgeted for it before any work was started on the extension.
 

Reply to Can you sign off any work with a 30ma RCD. in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock