Hi, my question is. If I have an old wylex consumer unit with NB type 2 breakers (not 60898). Or let's say any CU for that matter. If it's protected by a 30ma RCD, will that pass the cert?. Or for example will the use of old mcbs not be up to standard. Thanks
 
The installation needs to be in a safe condition to extend.
Any new circuits or alterations need to meet latest regulations.
It's theoretically possible to comply using a rewireable board.

Numerous questions come to mind, for for starters:
Where is the RCD installed, between meter tails and consumer unit, or at the start of the new circuit?
Has a surge protection device been installed?
Is the lighting in the extension RCD protected?
Is there a bath or shower room in the new extension?
 
No, new ring has been wired to a new extension at the back of the house and just needs an EIC.

The installation needs to be in a safe condition to extend.
Any new circuits or alterations need to meet latest regulations.
It's theoretically possible to comply using a rewireable board.

Numerous questions come to mind, for for starters:
Where is the RCD installed, between meter tails and consumer unit, or at the start of the new circuit?
Has a surge protection device been installed?
Is the lighting in the extension RCD protected?
Is there a bath or shower room in the new extension?
 
Thanks for the reply This is the puppy, RCD protecting all circuits in the house. Everything past this consumer unit meets regs. If RCD is testing fine and all other tests are fine. Would this be acceptable to sign off, or would most go down the consumer unit change route?
 

Attachments

  • Screenshot_2022-07-23-21-54-40-74_99c04817c0de5652397fc8b56c3b3817.jpg
    86 KB · Views: 29

Reply to Can you sign off any work with a 30ma RCD. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Ok, most new Consumer unit seem to come with a 63A RCCB and two MCBs. Most house consumer units now will also have RCD of some type be it a dual...
Replies
24
Views
1K
Hello All, I am a homeowner (but not an electrician) and I am renovating a house that has an old CU containing MCBs and an MK LN5725 residual...
Replies
5
Views
855
Afternoon everyone, I have a quick question about the Tesla Gen 3 Wall Charger? Does it require Type A 30MA RCD protection or not. Only because...
Replies
3
Views
1K
This is a strange one, my neighbour is a bit mad, he had a largish extension built in about 2015, the builder attempted to do everything including...
Replies
3
Views
991
I try to keep out of Domestic work but I have a problem at home. Currently I have a wylex fuse board with re-wire fuses. they are great because...
Replies
55
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock