Search the forum,

Discuss CAT 7 problems in the Computer and Networking Forum area at ElectriciansForums.net

M

Maddison

Recently finished 1st fix, carried out some tests just to give us an idea of possible problems and a lot of the CAT 7s are failing due to twist ratios. CAT 6s are passing fine, any advice or similar experiences ?
 
What tester are you using, Fluke DTX?
What test standard are you testing too?
Cat 7 should only be used with GG45 connectors if you want Cat 7 performance.
What are your failed results failing on, NEXT?
What make of cable, outlets and patch panels are you using?
Why are you using Cat 7? It is not ratified yet, so in theory there is no test standard. Please don't say future proofing...

I install Cat 7 Nexans Marine on Oil Platforms and Vessels, but terminate it with Cat 6A connectors and then test it to EN11801 Class Ea (cat 6a). Clients ask for Cat 7, but don't have a clue what it will give them.
 
It's on a new prison build in Australia so blame the government for wanting the CAT 7 lol, yeah it's a fluke DTX 1800. Seems to be the jacks at this point in time as after abit of investigation a little tweak in the jacks were going from pass to fail so easily. TE connectivity/AMP are the product being used.
 
TE are a good make, although AMP are their budget range. Terminations have to be spot on for this, keep cable bend radius within spec, and don't use undue force pulling them in. What Standard are you testing to?
 
after testing cat 6 have you changed from class E to class F and reset the referance, just a thought , have you selected cat7 as well as class F and selected the correct NVP %, Siemon would ask us to change the NVP to 68% when testing their cat6 cable. Another thought could be other contractors especially the security guys who think the catinary wires you have spend all week fitting and looming with velcro deserve all their cables on as well with some nice tight cable ties, cut many the security cables off our looms. Have you set the test limits at ISO 11801.
 

Reply to CAT 7 problems in the Computer and Networking Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock