Search the forum,

Discuss Central heating thermostat in the Central Heating Systems area at ElectriciansForums.net

We can only guess at what all the wires are.

The fact that it’s in a pattress and not a proper joint box… we have no clue what diagram the installer was following.
 
We can only guess at what all the wires are.
Looking at what terminals the valve is connected to greatly reduces the number of unknowns.
Terminals from left to right: Hot water on from timer to cyl stat, Hot water off from programmer and cyl stat, Boiler call for heat, Heating on from programmer to room stat, Heating call from room stat, Neutral. The last one could be permanent live or pump overrun from boiler. The block on its own earth.
 
We can only guess at what all the wires are.
But it's much more fun this way! In fact Danfoss 3 port zone valve wiring is a known entity and has stayed the same luckily even for 30+ years!
As per @freddo 's comments:
Grey is Hot Water Off
Brown/White is Heating On
Blue is Neutral
and Orange is the output signal to ask the boiler to fire up.


1672688679345.png


So with 100% certainty we can say that with the Heating set to ON and stat all the way up then 2 and 3 should measure 230v to Neutral (marked)
I agree with Brian and Freddo that 1 is the controller asking for heat. So this should also measure 230v to Neutral.
Obviously this needs doing very carefully.
That will quickly reveal what is going on.
 
1) when you call for heat does the boiler kick in when the time clocks on.
Does the boiler kick in when you
Turn the stat on
2) does the stat on the cylinder call for hot water
3) does the hot water comes in.
Zone valve work from the time clock
Does the valve move.
Is it a two chanel time clock.
 
Last edited:
But it's much more fun this way! In fact Danfoss 3 port zone valve wiring is a known entity and has stayed the same luckily even for 30+ years!
As per @freddo 's comments:
Grey is Hot Water Off
Brown/White is Heating On
Blue is Neutral
and Orange is the output signal to ask the boiler to fire up.


View attachment 105004


So with 100% certainty we can say that with the Heating set to ON and stat all the way up then 2 and 3 should measure 230v to Neutral (marked)
I agree with Brian and Freddo that 1 is the controller asking for heat. So this should also measure 230v to Neutral.
Obviously this needs doing very carefully.
That will quickly reveal what is going on.
Fantastic, thanks Tim I'll check this tomorrow. Thanks Buzz I'll reply to your helpful questions tomorrow too.
 
I'll test the wires later today when I get home from work but I have a quick question to ask. Would the wiring on my thermostat accommodate one of these digital/programmable units such as this?
 
Would the wiring on my thermostat accommodate one of these digital/programmable units such as these
It looks like you may have the neutral present at the stat, that some installations lack, but in my experience of 'stats similar, but not identical, to the one in the link, it might need a permanent live to preserve its programming, which will need the 'stat wiring to be arranged so that is is before the programmer instead of after.
The one's I have in one of my properties will default to their 'off' position if their power is interrupted.

Edit: Also worth noting that there are two types of these kinds of 'stats. Ones with the temperature sensor built in, and ones where they connect to a remote temperature sensor on a 2m or so lead.
 
It looks like you may have the neutral present at the stat, that some installations lack, but in my experience of 'stats similar, but not identical, to the one in the link, it might need a permanent live to preserve its programming, which will need the 'stat wiring to be arranged so that is is before the programmer instead of after.
The one's I have in one of my properties will default to their 'off' position if their power is interrupted.

Edit: Also worth noting that there are two types of these kinds of 'stats. Ones with the temperature sensor built in, and ones where they connect to a remote temperature sensor on a 2m or so lead.
Is that the blue wire for neutral, Brian, I don't think that's connected at the junction box.
 

Reply to Central heating thermostat in the Central Heating Systems area at ElectriciansForums.net

Similar Threads

At the moment it depends on the weather on how well the central heating works, the main problem is the Nest Gen 3 thermostat only measures the...
Replies
7
Views
741
Hey everyone, hope you all had a good xmas. Got called around to change over an old style pin type thermostat to a hive one for a family member...
Replies
1
Views
633
I have a Firebird oil boiler that is controlled by a Honeywell timer (no thermostat) that has channels for hot water and central heating...
Replies
8
Views
486
I have a fully pumped Y plan heating system using a Potterton EP2 programmer. Drayton MA1 Diverter valve. I have just replaced the Actuator head...
Replies
4
Views
678
It has become a common occurrence that my boiler is failing to respond when the thermostat kicks in. I hear an audible click from the heatlink...
Replies
16
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top