Search the forum,

Discuss Clamp meter that will measure milli amps in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
8
Afternoon all. I’m looking to invest in a clamp meter but want want that will measure milli amps (nuisance tripping etc). The megger 305 seems the best about; is there any others out there? TIA.
 
look for the resolution. think it's 0.1mA which is fine for tracing earth leakage.
 
So is that one any good then?
You get what you pay for.
(Drop unknowns on the floor = drift)
( compare with a "Known" situation at home for some stability )
But you could pay for quality - and have it banging about in the van -little used for years !
(With all this DC type RCD/RCBO changes ,I'm still unsure what is around the corner)
 
fluke771.jpg
Fluke709.jpg




I use one of these. Being able to move the clip separately is handy. Just make sure it pointed in the right direction. I often couple it up with the other one for signal faults, Fluke-709 | Fluke 709 Multi Function Calibrator | RS Components - https://uk.rs-online.com/web/p/multi-function-calibrators/7769529/ . Very handy if you carry out fault findingfluke771.jpgFluke709.jpg on your own.
 
@Haworth
Just in case you didn't realise, David is having a bit of fun with that recommendation. Don't clamp a 771 around an AC line, it... won't appreciate it.

As for AC leakage clamps, I use an AEMC model 565. It has a high range to 100A AC, low range to tens of microamps.
 
View attachment 51091View attachment 51092



I use one of these. Being able to move the clip separately is handy. Just make sure it pointed in the right direction. I often couple it up with the other one for signal faults, Fluke-709 | Fluke 709 Multi Function Calibrator | RS Components - https://uk.rs-online.com/web/p/multi-function-calibrators/7769529/ . Very handy if you carry out fault findingView attachment 51091View attachment 51092 on your own.
just seen the price.could buy a van and a MFT for less.
 
My current clamps are :
fluke clamp 1:1000 ratio producing 150A from150mA DMM output
Fluke 360 reading from 1uA to 60A brilliant for tracing fault currents.

29AD4CEC-38F0-4A93-80EE-0EBC3A477F1D.jpeg
CFD2656E-5387-4ABF-B1EC-046B376AD26B.jpeg
 


If you haven't the money for Meager or Fluke.

This Martindale is a good all rounder

I believe this guy sponsors the forum and he even gives an added discount to members.
 


If you haven't the money for Meager or Fluke.

This Martindale is a good all rounder

I believe this guy sponsors the forum and he even gives an added discount to members.
The unit you’ve linked to costs more than the Megger DCM305E
 

Reply to Clamp meter that will measure milli amps in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock