Search the forum,

Discuss Coding question - 8.5kw shower, B32 in the Electrical Testing & PAT Testing Forum area at ElectriciansForums.net

Pretty Mouth

-
Esteemed
Arms
Reaction score
2,874
How would you code this?

A 8kw shower (so pulling ~37A) is protected by a B32 breaker. 6mm² cable rated at 47A, ref method C
(Actually, that last bit isn't true. In fact it's currently ref 101 = 27A, but an easy fix to get it to ref C, so for the sake of the discussion, let's pretend it's ref C)

I'm torn between C2 and C3. I suspect it's technically a C2, but after at least several years like this (date on shower 2014, circuit installation date 1997), and with no apparent ill effect on any of the equipment, I find it difficult to sell it to the client as potentially dangerous.
 
I think C2 is more appropriate personally, as the circuit breaker is subjected to a sustained overload every time the shower is used and may eventually break down. Albeit the shower may be in use only for short periods.
 
I think this is where inspection is so important. If there is no thermal damage after years of use then C3. The section in insulation more than 100mm deep is a good spot to look - move and replace if necessary.
I had a look at the cable under the insulation and it seemed fine, there was no visible signs of damage. Tested fine too. I'd bet money that there's nothing wrong with it.

I went to replace a shower a few months back, but ended up having to rewire the circuit. Again a 32A breaker, ref 101, but this time 4mm T+E with a 9.5kw shower! Out of curiosity I cut open the old cable where it had run under the insulation, to have a good look at it. You wouldn't be able to tell it from new, it seemed mint apart from it being old colours red/black.
 
Did you mean it that way around? I can assure you that a fixed resistive load will draw more current on 240V than on 230V.
I'd stick a clamp meter on it before deciding any further.
I think what Tel meant is shower MI's usually give the shower rating for running at both 230V and 240V. I didn't specify which. Eg, Triton Aspirante 8.5kw shower would draw 8.5kw at 240v, or 7.8kw at 230v
 
the current is dependant on voltage and resistance as per ohms law. a 8.5kW shower wiill draw 35A at 240V to achieve the wattage. drop the volts to 230V and the kWs will be lower as the current drawn depends solely on the resisitance of the element and the voltage applied to same.
 
check the cable condition at CU, isolator and shower if no signs of thermal damage and it tests ok replace with B40 MCB or RCBO if needed. id code it C3 if no damage and tested ok
 
Not an opinion, but a question*

Some responses have mentioned that signs of thermal damage to cable (lack of in this case) would affect coding. What I can not help wondering is should the type of load be given consideration in this situation? What I'm getting at is the fact that the householder may take relatively showers in moderately warm water, but change of tennancy/ownership could see hotter showers, for much longer periods of time becoming the norm and could quickly and drastically change the physical condition of this circuit.

Should this be given consideration or does coding solely depend on what you find at time of inspection? Sorry for the interruption and please feel free to point out if this is simply daft.
 
Running the shower hotter doesn't make it use more power; it just means the water flow rate is less.
That doesn't apply to longer showers, of course, but an EICR is a snapshot in time, just like your car's MOT test.
Doesn't stop you adding comments if you think something might deteriorate in the future.
 
I’m sure I’ve completely misunderstood this thread, and I’ve read through it a couple of times, but I have had a couple of scotches.

We’re saying that, and I’m taking everything written as correct, that we have a cable rated at 47a, protected by a 32a mcb and we’re looking to give it a code 2? Have I got this right?

The other way round I would understand, but what’s the problem?
 
I’m sure I’ve completely misunderstood this thread, and I’ve read through it a couple of times, but I have had a couple of scotches.

We’re saying that, and I’m taking everything written as correct, that we have a cable rated at 47a, protected by a 32a mcb and we’re looking to give it a code 2? Have I got this right?

The other way round I would understand, but what’s the problem?
Not exactly. The cable is fine for the load, it's not a concern (or at least it won't be once i dig it out from the loft insulation).

The problem (or perhaps not) is that the breaker is rated lower than the load. Could, as @loz2754 suggests, repeated overload of the breaker over the long term cause damage to it that might result in danger?

I suspect not, but I don't know that for certain, hence the question
 
Well there's certainly a discussion to be had I suppose, but if we're talking about an EICR I don't see a problem, and I don't understand why you would look for damage to a cable being utilised below it's ccc.

Like I said, I've had a scotch, or 2, and I probably shouldn't be anywhere near a keyboard at the moment.

I'll have a look in the morning.
 

Reply to Coding question - 8.5kw shower, B32 in the Electrical Testing & PAT Testing Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock