Discuss Conduit and loft insulation? in the UK Electrical Forum area at ElectriciansForums.net

Gordon04

DIY
Reaction score
0
Hi,

Iam replacing my loft insulation to a thickness of 270mm, putting 100mm between the joists and then 270 over the top, then flooring it. I’m Putting 175mm loft legs on top of the joists which are 130mm which should give a slight air gap. My question is there is 20mm metal conduit running single cables to the lights and switches which is sitting on top of the joists, is the conduit permitted to be within the layers of insulation?

Thanks
 
should be OK with lighting as long as the lights are low wattage e.g. LED. however, singles in conduit is ancient. could it be time for a rewire?
 
should be OK with lighting as long as the lights are low wattage e.g. LED. however, singles in conduit is ancient. could it be time for a rewire?
Ought to o be easy to rewire in that conduit. Personally I'd use derating factors for whichever gives worse case (insulation I think) cable rating and adjust accordingly
 
should be OK with lighting as long as the lights are low wattage e.g. LED. however, singles in conduit is ancient. could it be time for a rewire?
Probably will be some sort of led bulbs.. they are the old colours so was thinking about changing them while I was at it, but was just going to keep it singles in conduit?
 

Reply to Conduit and loft insulation? in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock