Search the forum,

Discuss Consumer unit replacement issues in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Splitting the ring is all you can do in this circumstance.

I bet the customer doesn’t even allow you to move furniture to access sockets though.

Have you double checked your mates work? He hasn’t done something daft in the CU and got legs mixed up?
Possibility of faulty rcd? (Swap it for known good one) or is it an actual N-E fault. What was the IR result?
Thanks for the feedback.
Disconnected the ring in the CU and found a very low reading between N & E, causing enough imbalance to trip the RCD.
Original installation did not have RCD protection so the current flow wasn’t enough to trip the mcb.
I do not know what the original installer was thinking but the ring serves the entire house including underfloor heating.
I have suggested that when we can pinpoint the problem we disconnect that section and replace it with a surface mounted option. I suspect there could more than one fault, there have been a number of additions as when splitting the circuit both legs trip.
Hope this gives you an idea what is going on.
 
He’s a close friend and was very supportive during my cancer treatment, I’m ok now though.
Your Mate, has he offered any help, Advice or offered to finish off whathe should have sorted in the first place, even though he was a help during your illness this should be passed back to him, tell your client to contact him, after all he is to blame. should have made sure all was OK prior to swapping the CU and issued an EIC on completion of the CU swap, thus negating the need for an EICR. IMO.
 
Your Mate, has he offered any help, Advice or offered to finish off whathe should have sorted in the first place, even though he was a help during your illness this should be passed back to him, tell your client to contact him, after all he is to blame. should have made sure all was OK prior to swapping the CU and issued an EIC on completion of the CU swap, thus negating the need for an EICR. IMO.
Yes he has taken full responsibility and is in contact with the client
 

Reply to Consumer unit replacement issues in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock