Search the forum,

Discuss Consumer units in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
3
Hi guys.

Just need pulling into check on this one. I’ve been asked to wire an extension including new lights and sockets and SD’s ran from existing circuits in the house.

Now his mains was fitted in ‘15; a split load RCD mains, located in a hallway of plastic construction.

I’ve always understood that any consumer unit of plastic construct located in a hallway, final exit or combustible cupboard is a C2 issue, anything outside of that is C3. While I’m not running in new circuits I’m under the impression that any aspect of the circuit I affect from the mains to the final accessory must be up to current standard so am I right in thinking that I should advise it be upgraded or that I install a small sub-main that is within regs and provide new circuits from it.
 
No not necessarily, text from Best Practice Guide 4 Iss 5. (C3) - Is it sole escape route, are connections satisfactory (ie no evidence of burning/loose)? There may be other issue though eg IP rating that may also be considered!
• Presence of a consumer unit or similar switchgear made from combustible material (e.g. plastic) that is not inside a noncombustible enclosure and which is: - Located under wooden staircase, or - within a sole route of escape from the premises (Note: If unsatisfactory connections are found during inspection, this would warrant a code C2 classification to be recorded)
 

Reply to Consumer units in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock