Search the forum,

Discuss Cooker / hob wiring, is this right? in the DIY Electrical Advice area at ElectriciansForums.net

D

digitalspace

Hi,

We're starting to strip our mums kitchen in prep for fitting a new one. When I removed the induction hob I noticed that it was fed directly from the rear of the plug socket that was designated for her cooker. The socket is fed with 6mm cable direct to a cooker switch above the worktop.

I'm just wondering if this is the correct way to do things i.e. is it safe to have a 7KW~ load fed from the back of a normal plug socket (admittedly the socket being fed from a 40a mcb w/ 6mm cable seems good, but are the terminals of a plug socket designed to have the hob wired in too?).

While I'm here I have another question you may be able to answer! Our mum is having integrated appliances and I've read that you can either have a socket behind the appliance controlled via a DP switch above the worktop, OR you can have sockets that remain accessible for example you can 'hide' the sockets at the back of a cupboard where you're still able to get to them. For aesthetic reasons I'd prefer the latter option and so I was thinking you could run a 2.5mm radial from the 'ring main' socket (above the worktop) to behind one of the new cupboards and put a double socket there. Obviously we'd leave the a large hole in the back of the cupboard for access to the socket/appliance plugs.


pics say a thousand words etc

20131102_163553.jpg
20131102_163616.jpg



Any help is appreciated! :)
 
Last edited by a moderator:
A nice little one to kick Monday off!

…if this is the correct way to do things i.e. is it safe to have a 7KW~ load fed from the back of a normal plug socket

Not the ideal way of doing it as a cooker connection point could easily have been installed to replace the socket point but I don’t believe it is against any regulation. Setting aside the wiring compliance of the installation itself and just thinking of the actual design loading if used as a connector and not socket outlet ….

7kW cooker ~ 30A which with the std diversity for a cooker = 10A + 30% (30-10) = 16A. Lets call it 20A for good measure.

Std single socket is design rated for 13A across the terminals with a load (e.g. plug). In this case the rear terminals are just being used as ‘connector’ blocks so without any manuf advice I wouldn’t know what they are capable of but c.f. to standard junction boxes I would be surprised if the couldn’t handle at least 20A as a connector.

In a nutshell you’ve probably got away with it so far by good luck more than good design, so during your upgrade rid yourself of the single socket and get a proper connection unit installed.

I've read that you can either have a socket behind the appliance controlled via a DP switch above the worktop, OR you can have sockets that remain accessible for example you can 'hide' the sockets at the back of a cupboard

Your first option is the preferred method of doing it and is what is considered best design practise – you can isolate the appliance from a switch which is readily accessible above the worktop.

But there is nothing stopping you doing it the other way by having a socket outlet in a cupboard adjacent to the appliance. Other than no-one might know where it is, you have to empty the cupboard to get to it and you will probably have to unwire/rewire the plug to feed it into the cuboard if you want to do anything with the appliance!
 

Reply to Cooker / hob wiring, is this right? in the DIY Electrical Advice area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top