Currently reading:
corrugated metal roof with steel frame fixings

Discuss corrugated metal roof with steel frame fixings in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

Reaction score
12
just looking at a 50kW on a corrugated metal roof on a steel frame. It is crinkly tin, not trapezoidal, with some insulation sheeting underneath. The only fixings recommended so far are Schletter Fix E but they look fiddly to install and am yet to fins a uk supplier with some in stock.

Can anyone recommend a fixing for this? ideally we wanted self tapping hanger bolts but the only ones for metal frames I can find are Schuco but these are for trapezoidal finishes.
 
what's the depth from the top of the corrugated section to the top of the supporting horizontal Z bar sections?

We've done similar using cruciform mounting, with horizontal rails run all the way across above the horizontal Z bar supports, and fixed at regular intervals every 50cm or so using 6.5mm x 80 / 100mm self tapping bolts with the water proof washer, and some form of rubberised water proof mat under the fixings, using these schuco trapeze brackets, with the bolts tapping into the Z bar below. To be on the safe side for wind loading at the edges we usually extend the rails outwards beyond the edge of the panels to stop the wind being able to loosen the first fixing and then effectively unzip the array one fixing at a time.

SCH-256039.JPG

Then using the little L cruciform brackets to run vertical rails off them for landscape mounting of the panels
SCH-259928.jpg
 
Thanks Gavin, not sure what the measurement is yet as only had prelim meetings with the client.

We have some of the schuco left over from another project - would love to get rid of it but as we are on a sinusoidal (so i have learned today!) roof - on first thoughts, I wouldn't have thought that those would be suitable. Do you have any pics of the one you have done like this?

I have come across a company called Ejot who supply self tapping hangers for steel substructures. We are getting a sample so Ill let you know what we think
 
Last edited:
schuco do a 125mm hanger bolt, but be careful that they are not to long. you will have to drill an 6.7mm pilot into to the purling then self tap hanger bolt after, then attach the L bracket mount rails and make sure there level,
Gavin idea saves alot of time though there will be about 1400 stitching bolts to screw in.
 
there will be about 1400 stitching bolts to screw in.
indeed. and you've got to make sure they've all hit the Z bar as well really unless the metal sheet is thick enough to get a good enough fix into.

it's only about 20-30 seconds per bolt though, and we'd usually have one of us doing that solidly, another following up with the cruciform rails, and another pair starting at one end with the panels, then the first pair start on with the panels from the other end once the rails are all done and meet in the middle (we always allow at least one 50cm gap in the middle for access for cleaning, maintenance etc usually 3-4 on bigger arrays, plus it allows us to work from both ends inwards.
 
We do a fixing which is identical to the Ejot, but significantly cheaper. We stock 4 different sizes so you can be sure you have the correct amount of thread to go through the insulation layer and into the purlin by the required amount. Feel free to email for details if required.
Thanks
 
Cheers Spitfire - just asked Alex to send some tech info on the bolt. it is loads cheaper than Ejot and if you have them in stock then that is even better.

Do you have to pilot this one, or is it self tapping?
 
They are self tapping - meaning that they create their own thread in the metal purlin and so make a good fixing point. They are not self drilling, and so you do need to pilot hole each one. I believe you need a 6.7mm drill bit for each one. (This is the same as the Ejot)
We have 150, 175, 195 or 230mm all in stock. Thanks.
 

Reply to corrugated metal roof with steel frame fixings in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock