Could be getting sacked, got pictures, please advise

Discuss Could be getting sacked, got pictures, please advise in the UK Electrical Forum area at ElectriciansForums.net

D

davrejonas

Got called into to work today for a meeting, this was a first fix on a kitchen, had to do 2 that day and didnt get in the first till gone 11.30 so was rushing like mad, manager came in took some pictures and has gave us the following list, we had previously been told not to have more than one row of capping as outside zones so cables were bunched up, we were going like 100 miles an hour

pictures should be viewable at ImageShack® - Online Photo and Video Hosting
pic 1 fixing screw directly through capping causing burrs, any pressure put on wall on wall like tiles could result in breakdown of insulation and cables shorting out
cables ran with no protection against plastering trowel
evidence of sheathing being hammered to get into flat position pressure faults could happen
10mm earth cable stretched between box potential break down of continuity
pic 2 screw through capping i pre drilled this the opposite side to avoid sharps, you can see on pic
pic 3 wiring not protected
wiring crossed over causing potential pressure fault
cable held in position by screw,,,,,this was a wedge, i know its not great but not tight against cable
pic 4 screw through capping, no capping to protect cables crossed over,,, cable held in position by screw,,,,,,,this was a capping wedge then capping cut short
pic 5 cable no protection, chases very untidy.....

would like to know your thoughts, really wanna have a good argument for them tomorrow as got kids and cant afford to be dismissed, i know the screw wedge is bad but i think the rest are kinda just being picky
 
Picasso would be proud. A real artist, but I won't say one in a million. It's frightening to say that there may be others of the same standard, God forbid.
 
The thing that concerns me is how many instillations have been done like this and are lurking behind the plaster ready to cause mischief?

I am nowhere near as experienced as a lot on this forum but that takes the biscuit, I wouldn't even contemplate leaving a job like that.

Speechless.
 
I must say the forums' mood tonite is mean lol.
You lot must be shocked easily to be offended by the OPs' work , i've seen much much worse :-D
But im at a loss to say anything positive right now.
 
Biff there's just no need to do a job like that you couldn't walk away from that could you

Probably not no , a bit of pride in youre work goes a long way. But.....
I've done exactly the same kind of work as the OP before and its not nice - conveyor belt kitchen refurbs in council houses on an estate , main contractor breathing down your neck everyday , crap money , working under the threat of getting sacked if you delay the other trades , grief off the tennants etc etc...
I did it for 6mths and without doubt the crappest job i've had.
Theres been plenty of times i've cut corners under pressure so i'm not gonna have a go at someone else for it even if the work is poor.
 
Cheers for feedback I knew myself it was rough but not dangerous had no access from upstairs so running more cables than normal ,used to use 3 rows of horizontal capping got told not too . If that would have been plastered and tiled then what problem would there be . Screw in centre wasn't done blind was pre drilled. Get to office at 7 tools out half eleven get paid 4 hours. Happened day before , we wait for 4 hours and get one hour waiting time as gesture
 
sorry, mate, but if you think that standard of work is acceptable, then you're in the wrong trade.

Yeah sorry about any harsh comments pal but I'm afraid I agree with telectrix on this.
The amount of hours I've put in to make right someone else's mistakes is unreal.

And I'm self employed!

We all make mistakes now and then but at least put it right before you leave.
 
Had a job this week that threw me some curve-balls... Lots of taking floorboards up and installing MF boxes where I hadn't expected I'd need them. Out of pocket time-wise, but one very happy customer, plus I know that the job I did is the best that anyone could have done. I have a huge mortgage and 2 teenage kids so my reputation is paramount.

I cannot believe anyone would walk away from that job, whatever the reasons, so I'm assuming this is a wind-up.
 
I really hope this is a wind up.

However, to answer the OP's original questions

"could be getting sacked" Good, I am pleased to see that your gaffers have standards. IMHO the sack is you getting let off lightly.

"please advise" Firstly, put away your butchery kit and never look at it again. Then, I believe that some of the bus companies are taking on trainee drivers. I suggest you contact them. Finally, although I am no legal expert, it appears to me you have an excellent case for sueing whover suggested you work as an 'electrician'. You even have photographic evidence to support your case.
 

Reply to Could be getting sacked, got pictures, please advise in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock