Having spend my life in an industrial maintenance roll I seem to have forgotten all I learned, could somebody help me on this one.

Its a new build and I am looking at the demand, where am I going wrong.

Diversity for total demand

Curcuit MCB
Upstairs Ring 32A
Downstairs Ring 32A
Lighting Upstairs 1 (5 Lights) 6A
Lighting Upstairs 2 (7 Lights) 6A
Shower 8KW 35A
Cooker Oven 7.2kw 32A
Smoke Alarms x 2 6A


So apply diversity?

Ring
100% of largest then 40% of other = 44.8A
Lighting 66% of demand (100w) = 66% 0f 5.22a = 3.45A
Shower 100% = 35A
Cooker 10A + 30% of fl in excess = 16.39A
Smokes No diversity ?? = 6A

Total demand = 105.64A :confused: and I haven't got the spec for the boiler yet :)
 
The smokes will hardly use 6A.

I know but I wasn't sure if I could use the rating of the smokes or if I had to use the MCB size?? either way which rule of thumb would that be I would ad them up and multiply by 0.4 old school :D making 59.6A or your way 80.6A so confused I think I may go back to the world of maintenance .
 
Last edited:
Hi, how do you apply the diversity to a 10 way split load board? eg 100a main switch split with 63a rcd covering 6a, 6a, 16a, 32a and 32a mcb's then a 80a rcd covering 6a, 16a, 32a, 32a and 40a mcb's. Do you apply diversity to each split load at 100% largest and 40% smallest which is 56a for the 63a rcd and 74.4a for the 80a rcd, how does the 100amp main switch calculate against these 2 figures rhen as 56a + 74.4a is over the 100amps. Or do you disregard the rcds and calculate all the mcb's together against the 100amp main switch? which is 111.2a, but then this is over the 100amps to.

Also if i was to put in a second board for garage etc, how do you calculate the diversity for each board as the mains in fuse is 100amps to, eg if i put 2 or 3 boards on that after diversity they are both within the 100amp swith on the board in theory i can run upto 200-300amps, but as the mains in fuse is only 100amps how do you calculate so you dont overload the main fuse?
 

Reply to Diversity in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock