Domestic extention and smoke alarms

Discuss Domestic extention and smoke alarms in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
2
Afternoon all,

Ive looked at the building regs but can't seem to find anything, i remember reading something that said when fitting smoke alarms off a lighting circuit you need to put some form of isolation in, is that correct?

I'm also looking to install nest alarms, do they all need to be wired?

Thanks for your help.
 
No isolation needed between lighting and smoke alarms, but would be better all smokes on a separate circuit themselves.

I believe Nest alarms come in mains or battery versions. (could be wrong, never fitted one)
 
No isolation needed between lighting and smoke alarms, but would be better all smokes on a separate circuit themselves.

I believe Nest alarms come in mains or battery versions. (could be wrong, never fitted one)
I would consider it better practice to feed them off a lighting circuit. Obviously this is only appropriate for domestic systems (and not ones with a fire alarm panel).
 
I would consider it better practice to feed them off a lighting circuit. Obviously this is only appropriate for domestic systems (and not ones with a fire alarm panel).
If its a new install, smokes on separate.... Tag off the lighting if its an addition, and you cant get back to the board.
What if you were working on the lighting circuit? Turn off the smokes? I know theres battery back up, but i'd prefer full fire detection if I can get it.
 
This implies an isolator is a requirement for non-domestic arrangements:
Not sure what you would use in a domestic arrangement, the obvious thing would be one of the "emergency light test" style of key switches but typically they are grid ones (could put it along side another grid module to replace an existing light switch of course)

I agree with @Risteard that putting it on the light circuit is safer - if faulty they are more likely to have it fixed!
[automerge]1587819736[/automerge]
What if you were working on the lighting circuit? Turn off the smokes? I know theres battery back up, but i'd prefer full fire detection if I can get it.
True, but I guess the time spent with anyone working on lights is small.
 
There's no requirement for isolation in domestic.

Like i said, a new install, i would put smokes on their own circuit. Just for easy identification, separation of circuits etc.
Tapping off the lights isn't wrong, or right, or safer, or less safe... its just done a different way. Like socket radial vs ring.

I have actually tapped an attic light off the base of a smoke detector to get a feed, which was fed itself from the lights.... all the feeds were at switches i couldnt get down to.
 
Thanks for the replies.

Having a dedicated circuit for the extention is easy enough, it's more difficult in the house. For example, putting them on the first floor would be difficult with the loft being boarded and full, would installing battery ones linked to the wired extention ones pass building regs?
 
Thanks for the replies.

Having a dedicated circuit for the extention is easy enough, it's more difficult in the house. For example, putting them on the first floor would be difficult with the loft being boarded and full, would installing battery ones linked to the wired extention ones pass building regs?

That depends on the LABC. Some will, some wont. And depends on the make of detector. Aico mains can be retrofitted with a radiolink base, so can "talk" to the newer battery powered detectors
 
That depends on the LABC. Some will, some wont. And depends on the make of detector. Aico mains can be retrofitted with a radiolink base, so can "talk" to the newer battery powered detectors

I was looking into installing Nest
[automerge]1587820650[/automerge]
I think building regs stipulate mains wired battery back up for building alterations/extensions.


S
I think building regs stipulate mains wired battery back up for building alterations/extensions.
So it's only applicable to the extention not the whole house? If so, installing wired in the extention and battery in the house linked would potentially satisfy LBC?
 
No isolation needed between lighting and smoke alarms, but would be better all smokes on a separate circuit themselves.

Smokes should be wired to a regularly used lighting circuit, I believe this is the recommended method in the BS.
This is to ensure that any failure of the circuit is readily identified and rectified.

A dedicated circuit is unlikely to be noticed if it trips, or fixed with any hurry.
 
Smokes should be wired to a regularly used lighting circuit, I believe this is the recommended method in the BS.
This is to ensure that any failure of the circuit is readily identified and rectified.

A dedicated circuit is unlikely to be noticed if it trips, or fixed with any hurry.

I think the isolation is very much dependant on the local building control, attached is a document from temside stating it needs to be in place
 

Attachments

  • Screenshot_20200425_143339.jpg
    116.4 KB · Views: 8
Smokes should be wired to a regularly used lighting circuit, I believe this is the recommended method in the BS.
This is to ensure that any failure of the circuit is readily identified and rectified.

A dedicated circuit is unlikely to be noticed if it trips, or fixed with any hurry.
Approved Doc B and BS5839:6 cite an independent circuit or the use of a lighting circuit.
 
I think the isolation is very much dependant on the local building control, attached is a document from temside stating it needs to be in place
If it is coming from the lights, so you can't isolate it without no lights, then I would personally want to see some means of isolation.

You don't want it to be accidentally switched which is why I would go for a keyswitch sort, but I guess a FCU that is out of normal reach is another option (might be an issue for disabled access of course...). Hopefully others on here will know better!
 
I think the isolation is very much dependant on the local building control, attached is a document from temside stating it needs to be in place
I could be incorrect here but I believe the purpose of isolation was so as not to interfere with the lighting for maintenance and was quoted in Approved Doc B. This is no longer quoted in Approved Doc B so I would actually question that as they may be using out of date requirements.
 
So it's only applicable to the extention not the whole house? If so, installing wired in the extention and battery in the house linked would potentially satisfy LBC?
You'll need to clarify with your LBC. With a major alteration or extension to a property, BI's can get a bit picky, and start applying particular building regs to the whole property. I had to install & link fire alarms to my whole house (basic level), when I had an extension done some years ago. Has the extension had building regs plans done? It might show them on the drawings.
[automerge]1587824071[/automerge]
Smokes should be wired to a regularly used lighting circuit, I believe this is the recommended method in the BS.
This is to ensure that any failure of the circuit is readily identified and rectified.

I believe that it is actually either a lighting circuit or a dedicated circuit from the DB. But as I haven't a copy of BS 5839, I can't back that up factually. But you can search for the subject, which kinda confirms this;

 
Last edited:
Smokes should be wired to a regularly used lighting circuit, I believe this is the recommended method in the BS.
This is to ensure that any failure of the circuit is readily identified and rectified.

A dedicated circuit is unlikely to be noticed if it trips, or fixed with any hurry.
Both are acceptable methods in bs5839-6 tho rented properties and hmo if applicable ,it is seen as better to do it from the lighting for the very reasons you’ve stated.
 
Thankyou for all your responses, they've been really helpful.

I have a friend of a friend that works for building control for a different council, he's said that either way is suitable and building regulations are only applicable to the extention. I will try and run a new circuit that covers the whole house and not just the extention, although it could be tricky to get to some locations without chopping the ceiling.

A secondary question... I'm looking at installing Nest, does anyone else have a prefrance of detector? It's my own home so I'm happy to pay a little extra for better quality.
 
Thankyou for all your responses, they've been really helpful.

I have a friend of a friend that works for building control for a different council, he's said that either way is suitable and building regulations are only applicable to the extention. I will try and run a new circuit that covers the whole house and not just the extention, although it could be tricky to get to some locations without chopping the ceiling.

A secondary question... I'm looking at installing Nest, does anyone else have a prefrance of detector? It's my own home so I'm happy to pay a little extra for better quality.
It’s your preference, I understand Nest links into other products and WiFi , iPhone etc. Aico have an app, and are well respected fire alarm manufacturer.

Take your pick.
 
Thankyou for all your responses, they've been really helpful.

I have a friend of a friend that works for building control for a different council, he's said that either way is suitable and building regulations are only applicable to the extention. I will try and run a new circuit that covers the whole house and not just the extention, although it could be tricky to get to some locations without chopping the ceiling.

A secondary question... I'm looking at installing Nest, does anyone else have a prefrance of detector? It's my own home so I'm happy to pay a little extra for better quality.
Nest don't have heat detectors, and for this reason I would avoid them.
 
I love the Nest thermostat, but the smoke alarms and cameras are overpriced junk in my opinion.
[/QUOTE]
What product would you recommend? In terms of how they look I find most other products look great. Are there many product out there that have a heat/Co and smoke/Co?
 
Last edited:
What would you recommend Dave? Moat don

What product would you recommend Dave? I find most other look

What product would you recommend? In terms of how they look I find most other products look great. Are there many product out there that have a heat/Co and smoke/Co?

I've never judged a smoke alarm by the way it looks, it's there to save your life not look pretty.

I have always fitted Aico alarms and never had a problem with them. They have a range of single and multisensor alarms to suit all domestic systems.

Whilst combined smoke and Co detection doe snake some sense, it's important to remeber that CO alarms may need to be fitted in different locations to smoke alarms to achieve the correct protection.
 
I've never judged a smoke alarm by the way it looks, it's there to save your life not look pretty.

I have always fitted Aico alarms and never had a problem with them. They have a range of single and multisensor alarms to suit all domestic systems.

Whilst combined smoke and Co detection doe snake some sense, it's important to remeber that CO alarms may need to be fitted in different locations to smoke alarms to achieve the correct protection.
I agree that it's there for a purpose but if its in your own home surely you want the nicest product?

Ive used Aico previously and they've always been reliable.
 
I'd run smokes on their own circuit.
The reason being if the lights are ever isolated for whatever reason i.e light fitting change, earth fault etc, you still have that smoke alarm in operation if anything goes wrong.

But then again I'm only a trainee myself. ???

ZippyMo
 

Reply to Domestic extention and smoke alarms in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top