A quick search for earth tape didn't come up with much, though this thread was of interest.

I'll start by mentioning that I've led a sheltered life and only ever dealt with PME (TN-C-S) so never had to deal with earth rods.
At our church, we've had an inspection of the lightning protection system (LPS), and as I expected the report's come back saying it doesn't comply with LPS standards but "There are hundreds of churches with lightning protection fitted to just the bell towers & spires only, they do not comply with LP standards, but the limited zones of protection provided by them is accepted as the norm, as long as the earth resistance on the system is 10.0 ohms or below."
I suspect most of you are ahead of me here, needless to say our earth rod doesn't give 10 ohms. It's reading 230 ohms ?
Talking to one of the church wardens, he recalls when the current one was fitted. It was to replace another that he described as "about 4 foot long, and when the guy had hammered it in, there was still two foot sticking up out of the ground", adding that the guy said "that's about as good as you'll get" as he'd just hit rock.
I can't see much point trying to get any decent rods in the ground, so tape seems a better bet. I'm thinking if we hire a mini digger over a weekend, we should be able to get a decent length buried - and put some service ducts in while we're at it for other things we've been thinking about.
The good news is that this is on the north side of the church, never gets any sunlight, and as far as I know, never dries out ?

As an aside, I asked them for their guidance regarding bonding of the electrical earth to the LPS earth, their suggestion was that given the high impedance of the current earth, it would be rather pointless. Assuming we get a decent earth, it's my intention to bond as per BS7671.

So for those with experience of such things ...
Anyone got any thought what sort of length we'd need to bury ?
Pointers to guidance on how to calculate (or at least, guesstimate) in advance how much we might need ?
And assuming I get a decent earth, what's the correct way to connect a bonding cable to the LPS conductor (in the earth rod pit, to the tape down the building (below the test/isolation joint)) ?
If necessary I can probably borrow an earth rod test rig - I'm thinking I'll need one to test it afterwards and see what we've got, and also it might be an idea to measure the soil resistivity before we start.

Obviously if funds were plentiful we could just get someone in with a remit of "make it so". But funds, in common with most rural churches, are very much not plentiful ?

Thanks for any insight anyone can give.
 
I would suggest you install an earth mat or mats rather than just strips of tape, another option is multiple rods properly spaced and linked together.
There is a bit more to lightning protection than just burying pieces of copper in the ground as you need to consider possible step potential issues if a strike occurs and people are around, it would be worthwhile contacting ABB Furse, A N Wallis or one of the other lightning protection manufacturers for some technical advice and possible solutions
 
Thanks.
One thing that I think you may have overlooked is the finance side of things. It's not that we aren't prepared to spend what's needed, it's a case of there isn't money to spend. To put things in perspective, we had a good collection today - it reached 3 digits (just). The last few weeks it's not made 3 digits. OK, there is some other income, but as I think you can imagine, the bills for keeping a big old shed of a building in good order (not to mention the diocese wanting their contribution) quickly eats up what income we have.
Hence, in reality, getting in specialists is pretty much a last resort.

So at this point, I'm looking at whether there are reasonably easy ways to get down to 10 ohms.
Tape is definitely the easiest as it's a matter of dig a trench, drop it in, backfill and compact. It'll take a while to settle and get full contact, but it's the minimum of excavation.
Mat (yes I already know about the principle) would simply need massive amounts of excavation - though I suppose we could DIY a grid on a lareg grid (not that we have mush distance between the building and boundary wall on that side).
And rods are a non starter in our ground.

Hence asking if people have any direct experience - e.g. how much tape might we need to bury to get down to 10 ohms in damp soil ? Even a rough idea will give me something to go on.
 
If you take the formula for the cruciform shaped buried conductor (appropriately enough) plug in a typical 150 ohm.m earth resistance, it needs about 36m of buried 16mm^2 conductor (40cm deep, not very senitive to that parameter) to get to 10 ohms.


I think typically they put in a buried ring around the building so conductors come down at various places to join it and a few radial out of that. Will look for some resources I remember reading...
 
Interesting to read this thread - I used to live in Cumbria and was a former churchwarden and former deanery treasurer so I completely understand the financial side of it as well as some of the challenges of a rather rocky area!
I'm aware of one church having to solve this issue but they managed with two or three linked rods.

CEF sell bare copper tape with a csa of 75 sq mm, which should reduce the distance, I'll run the numbers for this later tonight if no-one beats me to it.
Out of interest - which area?
 
I was going to add that I'm not sure 16mm copper is acceptable for a LPS, as pointed out above typical tape is 75mm^2.

However, if you attempt the adiabatic for a 100kA 10us/350us lightning surge it is about 16mm! For radials off a higher current ring or similar attachment to the down conductor they may be OK. The earth resistance is not so impacted by CSA, more total length.
 
I've now used formula d from the link that @pc1966 provided which is a straight run of a conductor.
I think I've got this right, I've included the formulas in case you want to recreate it (or so someone else can point out any mistakes!).
It seems to suggest that again with soil resistivity of 150 ohm-meters, 21 metres of 75 sq mm csa tape buried 50cm down would get you to 9.9 ohms.
(If you install all 25m in the pack it comes out as 8.69 ohms)

The main variable is the resistivity of the soil and as you say it's worth checking that in advance.

1621801096889.png
 
I've now used formula d from the link that @pc1966 provided which is a straight run of a conductor.
I think I've got this right, I've included the formulas in case you want to recreate it (or so someone else can point out any mistakes!).
It seems to suggest that again with soil resistivity of 150 ohm-meters, 21 metres of 75 sq mm csa tape buried 50cm down would get you to 9.9 ohms.
Yes, much as I do for linear tape.
(If you install all 25m in the pack it comes out as 8.69 ohms)

The main variable is the resistivity of the soil and as you say it's worth checking that in advance.
The soil is always the dominant unknown!
 
It always amaze's me that the richest land owner in the UK can't afford to do the job itself.
You'd think, but in fact the land owner has absolutely nothing to do with it in practise.
The short version of a very complicated arrangement is that a local C of E church usually gets a vicar/priest in charge (often shared between several churches these days) and a house for them to live in provided. They are actually the only things a local church doesn't have to fund itself.
All other costs, utility bills, insurances, repairs etc. have to be paid for out of local funds. The only income is what a congregation give and gift aid on it. It also has to pay a fee to C of E based on a complex formula which is typically at least £50k+ a year as a contribution towards housing and employment costs and pension costs.
So locally many churches are pretty skint, it all depends on the disposable income of the people who attend them.
I can totally see why it would appear differently at face value though.
 
The Church of England has it all ways it would seem, get everyone else to pay for everything, I think if they sold off a few assets, like the City of London, they could pay for their own upkeep and not keep sponging off the congregation.
 
The Church of England has it all ways it would seem, get everyone else to pay for everything, I think if they sold off a few assets, like the City of London, they could pay for their own upkeep and not keep sponging off the congregation.

I believe people give to churches of their own free will.

Long time since I've been through the door of any, but it always seemed to me that donations were optional.
 
Back to my original numbers, seems they suggest "50 mm2 stranded conductor (minimum strand size 1.7 mm diameter)" as an option (page 57, along with others), might be cheaper / easier than 25 x 3mm = 75mm^2 tape.

£5.36/m just now from here:
 
The short version of a very complicated arrangement is that a local C of E church usually gets a vicar/priest in charge (often shared between several churches these days) and a house for them to live in provided. They are actually the only things a local church doesn't have to fund itself.
All other costs, utility bills, insurances, repairs etc. have to be paid for out of local funds. The only income is what a congregation give and gift aid on it. It also has to pay a fee to C of E based on a complex formula which is typically at least £50k+ a year as a contribution towards housing and employment costs and pension costs.
So locally many churches are pretty skint, it all depends on the disposable income of the people who attend them.
I can totally see why it would appear differently at face value though.
That's a reasonable summary.
The best bit is how (certainly in our case) the church and the vicarage were built with funds raised locally, but then at some point the CoE changed the rules such that they now own the vicarage, and if the church closes, they get to take the building and grounds.
So locals paid to build it, locals pay for it's upkeep, but if it closes, the locals don't get to keep it !
And we don't even get to include the rent (whether real or nominal) from the vicarage that we used to own as part of the parish offer (the fees referred to).

I believe people give to churches of their own free will.

Long time since I've been through the door of any, but it always seemed to me that donations were optional.
Yes indeed.
And that's getting ever harder as congregations dwindle - in many cases, as they die off. There are a few that are doing well, but in general, rural parishes are struggling. At present we have several locals who are quite generous and we just about make ends meet - but given their ages ...
We're trying to re-organise the church so the building can be used for other things - as they used to be before the Victorians decided otherwise and inflicted pews on people. We're lucky in that (after getting rid of the pews and some other works) we have a space that will be suitable for many uses - big rectangular box without loads of pillars in the way. But it'll cost a fair bit to do that, but it's realistically the only way that it'll survive - it won't survive on what the locals choose to donate.

As to the original question, a bit more reading to do ?
 
That's a reasonable summary.
The best bit is how (certainly in our case) the church and the vicarage were built with funds raised locally, but then at some point the CoE changed the rules such that they now own the vicarage, and if the church closes, they get to take the building and grounds.
So locals paid to build it, locals pay for it's upkeep, but if it closes, the locals don't get to keep it !
And we don't even get to include the rent (whether real or nominal) from the vicarage that we used to own as part of the parish offer (the fees referred to).


Yes indeed.
And that's getting ever harder as congregations dwindle - in many cases, as they die off. There are a few that are doing well, but in general, rural parishes are struggling. At present we have several locals who are quite generous and we just about make ends meet - but given their ages ...
We're trying to re-organise the church so the building can be used for other things - as they used to be before the Victorians decided otherwise and inflicted pews on people. We're lucky in that (after getting rid of the pews and some other works) we have a space that will be suitable for many uses - big rectangular box without loads of pillars in the way. But it'll cost a fair bit to do that, but it's realistically the only way that it'll survive - it won't survive on what the locals choose to donate.

As to the original question, a bit more reading to do ?

Seems like a very un-Christian way of doing things.
 
We're trying to re-organise the church so the building can be used for other things - as they used to be before the Victorians decided otherwise and inflicted pews on people. We're lucky in that (after getting rid of the pews and some other works) we have a space that will be suitable for many uses - big rectangular box without loads of pillars in the way. But it'll cost a fair bit to do that, but it's realistically the only way that it'll survive - it won't survive on what the locals choose to donate.
There's one in my nearest town that's a standard size church, about 150m from another standard size church, both C of E, so they've basically 'mothballed / preserved' one of them and it now gets used for various events, small theatre etc. And curiously, they advertise overnight B&B, too, something called Champing, I think.
 
I don't think this has a large enough surface area for what's required. The minimum lattice mat or solid plate size is 600x600 for lightning conductors and there isn't any guidance for things like this.


I was thinking along the lines of the stuff being used in addition to other means of earthing to increase area and help reduce Ra
 
I was thinking along the lines of the stuff being used in addition to other means of earthing to increase area and help reduce Ra
Don't get me wrong it probably would help. I just have a biased opinion to the traditional methods and I honestly haven't tried anything else. All we use is rods, mats, ring tape or foundation earthing. It's not an industry that modernises quickly unfortunately.
 

Reply to Earthing with solid rock below surface - burying tape for lightning earth in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock