Search the forum,

Discuss EICR Code for two circuits on one cable. in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Reaction score
0
Hi,

Currently undertaking an EICR on a factory, we have came across an 4 core SWA and 4 Core SY which have been split in the DB to serve two separate circuits. The SWA has the Brown on a 10A MCB and the Grey is on a 16A. So clearly they have shared earths and shared neutrals, similar scenario with SY. What code fault would you put this down as?
 
Have they definately got a shared neutral between the 2 circuits on the SWA?
Normally when using a 4 core SWA for 2 circuits there would be 2 lives, 2 neutrals and a shared CPC (the armour) which is fully compliant.

However with a 4 core SY (assuming that is 4 cores total not 4 cores plus earth) that is obviously not possible.
If they have used a shared neutral between 2 circuits I would code it C2.
They may alternatively have connected the cores as seperate neutrals and used the braid as a CPC which is also unacceptable and would attract a C2 code.
 
With the SWA being on two separate phases and different size MCB’s surely that can’t be compliant. We haven’t traced the cable as of yet but presume it goes to a Joint Box.
 
With the SWA being on two separate phases and different size MCB’s surely that can’t be compliant. We haven’t traced the cable as of yet but presume it goes to a Joint Box.
If it has a 'borrowed neutral' (common N to the two circuits) then it is C2 no matter what, as above.

It should be labelled as having more than one point of disconnection at either end.

Otherwise it is not elegant, but you see multiple singles in conduit doing much the same idea.
 
It should be labelled as having more than one point of disconnection at either end.

I don't think there's any requirement for a cable carrying multiple circuits to be labelled as such, only equipment which cannot be isolated from a single device.

Otherwise it is not elegant, but you see multiple singles in conduit doing much the same idea.

It can be an elegant soloution. Working in theatre/stage lighting circuits are usually in multiples of 6 so it is quite normal to use muticore SWA to carry multiple circuits to the same place.
 
I would go with an FI until you can put sufficient resources to identifying the conductors and feed arrangements for the circuits. This will have the same end result as a C2 and would give an unsatisfactory EICR. You could add into this "Unsatisfactory pending further investigation of circuit wiring for circuits X"
 
Hi,

Currently undertaking an EICR on a factory, we have came across an 4 core SWA and 4 Core SY which have been split in the DB to serve two separate circuits. The SWA has the Brown on a 10A MCB and the Grey is on a 16A. So clearly they have shared earths and shared neutrals, similar scenario with SY. What code fault would you put this down as?
You need to identify what the situation is before you can apply the correct code (if one is required at all), else your report maybe inaccurate, if not it may require further investigation. Is your statement (my bold) an assumption or verified as true?

As westward10 stated - "Providing the circuits are electrically separate including the neutral conductors and the insulation of the conductors is rated for the highest voltage then it is fine".
 

Reply to EICR Code for two circuits on one cable. in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K
Another thread asked about two circuits sharing a common multi-core cable and regulation 521.8.1 was mentioned. A friend of mine has inherited...
Replies
13
Views
718
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
968
Afternoon all, Just wondering what everyone's response to the following scenario is. Letting agents have asked us to carry out an EICR. There was...
Replies
42
Views
5K
Morning all So the site I'm based at recently had some work done (think partitioners). This package of work included electrical. This was...
Replies
47
Views
8K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock