Search the forum,

Discuss Electric Hob Diversity. in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
28
Hi colleagues

A friend of mine has purchased this electric hob for his kitchen.


It shows on the spec that it has to be hard wired by a spark.

So after calculating the amperage (5400÷230), I'm getting 23.4amps.

Will diversity have to be applied just for a single hob? Or is it only for a cooker which includes 4 or more hobs, oven and grill?

Any help will be appreciated.

ZippyMo
Trainee Spark.
 
A quick search find a copy of its manual on-line, they say:

"This appliance must be wired into a 30 A double pole switched fused spur outlet, having 3 mm contact separation and placed in an easily accessible position adjacent to the appliance. It should not be located above the appliance and no more than 1.25m away from it."

Then they go on to say to use "H05 RRF 3 core x 6 mm" cable but I would be pretty sure the 07 rating is fine, for example:
As you say, looking at a bit of a delay just now...

Edited to add, found it here:
Just noticed its not exactly the same part number, so wise to double-check when you do get it. Odd that Baumatic's own service site is not listing that model!
 
Last edited:

Reply to Electric Hob Diversity. in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock