Currently reading:
Electric Underfloor Heating Installation

Discuss Electric Underfloor Heating Installation in the UK Electrical Forum area at ElectriciansForums.net

Midwest

-
Esteemed
Arms
Reaction score
10,616
I've been asked to install some electric underfloor heating, as part of a bathroom refurb. Never installed the stuff before myself, in fact 'cos of some of the nightmare stories I've read here, I've managed to avoid it. However, got to do it this time. I was wondering if those that have put some in, could offer some installation tips, or do's & don'ts.

Customer will be providing the matt & controls, he wants a particular thermostat, which is WiFi connected. I don't know the manufacturer at the moment. The heating is going in a small 1st floor ensuite, about 2m square and may have a tiled walk in shower. He wants the tiled shower area heated, which I'm not sure is possible, due to the gradients of the base?

I've read about testing continuity before and after tiling. Subfloor will be chipboard overlade with 18mm ply, and whatever tanking is required. I see that most manufacturers suggest installing conduit for the sensor, what do you use?

Advice appreciated.
 
my top tip is don't let the customer supply the parts .....

you need a decent stat, and a matt which is laid out on a backing - avoid the ones which you have to layout in one core all around the area....

Call a manufacturer like WarmUp and see what they say about the shower area.

Who is doing the tiling?
 
Thanks Murdoch, I understand the parts thing, but the guy is a bit of a geek, and wants a particular controller so over to him. Should get the matt manufacturer today.

Doing the job for my son's business, so they have a tiller.
 
Try to map out exactly where the sensor is going in order to make sure a groove is made for the supplied ducting (12mm roughly) and consider putting in two sensors, one as a spare. They do go and its a failsafe back up. Manufacturers will say if it's 2 sq m. then get 1.5 sq. m. However measure very carefully, although you need to leave a space around the edges and obstacles you should attempt to get it as close to all edges as possible. If it's a hard shape you can get two smaller mats as the controller can control more than one mat.
 
Try to map out exactly where the sensor is going in order to make sure a groove is made for the supplied ducting (12mm roughly) and consider putting in two sensors, one as a spare. They do go and its a failsafe back up. Manufacturers will say if it's 2 sq m. then get 1.5 sq. m. However measure very carefully, although you need to leave a space around the edges and obstacles you should attempt to get it as close to all edges as possible. If it's a hard shape you can get two smaller mats as the controller can control more than one mat.

Is that two in one ducting or two separate sensors & ducting :oops:? Do all manufactures supply a ducting?
 
Apart from what's been mentioned I always take a photo of the mat once it's laid and do a sketch of the layout.

We had a builder install a heat mat recently, and they ended up putting the floor prob to close to the mat, so the stat kept cutting out as it thought it was up to temp.

They managed to speak to techinical and set the stat to work on air temp only, but we omitted it on our EIC because in Section 703 it says about the the floor temperature itself needing to be limited to 80°C, and the system should be able to limit the floor surface temperature in areas where people will walk.
When we phoned techinical they said this could be only achieved by using a floor probe.

So hopefully your customer gets the right stat, another thing is I believe different manufactors use different resistances for their floor probes.
 
My customer is using 'thermonet' heat matt & their 'thermostouch'; thermostat Underfloor Heating - Thermogroup - http://www.thermogroupuk.com/products/underfloor-heating/. The manufacturer also do a matt specifically for shower trays to accommodate drainage, and are IP68 rated. Still not convinced on how the matt can be formed, to follow the contours of the drainage for walk-in showers (tiled), but guess its flexible. Need to speak with manufacturer & customer about that. Matts supplied with flexible conduit for sensor.

Instructions for testing before during installation etc.

Seems a piece of ---- :rolleyes: (note the sarcasm smiley!)
 

Reply to Electric Underfloor Heating Installation in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock