An extraneous-conductive-part or earth rod? One must remember being told as an apprentice you can't have earth rods on a TN-C-S supply, it was the trick question, as any earth rod was called an extraneous-conductive-part.
But with any cable there needs to be a current rating and traditionally with PEN it was 10 mm² but with TT it could be far smaller, and what we need to consider is will the cable take the earth current.
So in a workshop all bonding conductors were 25 mm² to ensure they would not melt, in that case it was due to welding currents, but the same applies to any PEN supply, had that friend used 16 mm² then likely it would have not melted and all would have been fine.
But in real terms we use resistors when connecting two earth systems, I have only seen it done once at point of aye gas terminal a box around 4 foot square had a massive resistor and the DNO earth and site earth were connected across that resistor so even if the DNO earth went to 230 volt nothing would burn out.
Clearly a single rod or 60 Ω is not going to allow enough current to flow to cause a problem, and if you have a water pipe connected at every house then because any fault is shared again no real problem, only when the site has really good earthing system is there likely to be a problem.
However just like when measuring the loop impedance in the main lower the better but if the prospective short circuit current exceeds the rating for protective device 4.7 kA or 10 kA then we may need a fuse or moulded breaker to take the fault current, the same applies to an earth, there is such a thing as an earth being too good.
Thing is I have never seen a fuse in an earth, only answer is a resistor, and as with many things because I have never needed to work out the size of a resistor I have never looked at how one works it out.