Currently reading:
First Aid safety signs | electric shock procedures required

Discuss First Aid safety signs | electric shock procedures required in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

S

silure130

hi
Is there a requirement for First Aid safety signs | electric shock procedures to be positioned near a distribution board. I have been to a remote pumping station and there are no safety signs anywhere. Would you put this down as a C3?
thanks
 
hi
Is there a requirement for First Aid safety signs | electric shock procedures to be positioned near a distribution board. I have been to a remote pumping station and there are no safety signs anywhere. Would you put this down as a C3?
thanks

There is NO requirement for this in BS7671:2008 Amt 1, so does not need a coding. You could argue that they should be displayed in an industrial workplace to meet HSWA:1974 and therefore include that as a comment in the appendix to your EICR.
 
Last edited by a moderator:
I was looking at a Allianz Cornhill report at a site I went to last week and saw it was put down. I will leave it out and mention it to the H&S guy who works for them.

thanks
 
I was looking at a Allianz Cornhill report at a site I went to last week and saw it was put down. I will leave it out and mention it to the H&S guy who works for them.

thanks
Have a chat with the H&S bloke before submitting your report. He may ask to get it put on there for justification to get the signs put up.
 

Reply to First Aid safety signs | electric shock procedures required in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top