Raptor0014

Esteemed
Reaction score
1,261
Did my first consumer unit change yesterday.
A few dodgy things with the old board as I’m sure most will see.

Owner wanted bringing up to date with individual circuit RCD protection and surge protection.

So fitted a Fusebox 10 way RCBO board. Complete with surge protection.

Also removed the bell transformer that was being fed from a hole directly in the side of the CU and put the cooker cable into some conduit as the owner didn’t want it chasing in. I didn’t think it wise to leave it draping over the top of the CU like it was previously!

Any feedback is welcome as I’m always happy to learn from the more experienced amongst the forum.

Only thing I couldn’t seem to rectify is the slight leaning of the RCBOs/Main switch. No matter what I did as soon as I torqued everything up on the busbar it moved slightly.

One of the RCBO was a tad close on testing as you can see on the pic. But a pass is a pass and I tested that both at the board and at a socket (was on a Ring Final).

Anyhoo here are some pics.
C7DE9622-7934-44D3-8F86-0D824D4B6D89.jpeg
94E9EC2A-7FAC-4195-8250-311C72078E0E.jpeg
4EA7914E-843C-4007-BA3A-AB0A0B2EF814.jpeg
27DBD3AD-44C3-4FC9-AFF3-6ABEF5EFFA33.jpeg
9AFC177C-4103-4D5F-B608-2696271DF146.jpeg
90531D46-106B-4CB2-9BF9-400BEAEEC930.jpeg
30748230-A35C-4DA2-AFA9-288A284ACC4B.jpeg
0701D4FD-5696-4F6E-96A2-9230E1BE30CC.jpeg
23B84E49-3BB5-4948-94FA-47732EC978BE.jpeg
8869AA11-7326-4916-8F6B-C04A3B3149D5.jpeg
64189C8F-90DF-48C5-8C7B-D3DD3233FA8C.jpeg
 
Can you give a valid reason for this.

I'd always understood that highest loads should be placed closest to source of supply and accepted that without question. In the last few years I've read opinions that suggest there is no reason to do this and that it is better to populate a board by ensuring higher loads are separated to allow efficient dispersal of heat.

Not really in a position to comment, but the latter makes more sense and I'd be interested to read thoughts on the matter.
 
I'd always understood that highest loads should be placed closest to source of supply and accepted that without question. In the last few years I've read opinions that suggest there is no reason to do this and that it is better to populate a board by ensuring higher loads are separated to allow efficient dispersal of heat.

Not really in a position to comment, but the latter makes more sense and I'd be interested to read thoughts on the matter.
i agree. i never place 2 High load MCBs adjacent.
 
Type AC are being phased out it would seem. I only fit type A these days.
Stopped fitting them years ago. I don't personally see any merit in fitting Type AC anymore. For no (or minimal) extra cost with many brands it's a no brainer. That said, the FuseBox ones are substantially dearer than their Type AC, but thankfully I think they might be withdrawing the Type AC. There are neutral switching Type A compacts with FuseBox - so these are what I use when using that brand (although they are dearer).
 
The MEM add on RCD pods, MR30s don't like being tested at the board. They refuse to trip when tested. Apart from these, I always test RCDs at the board, preferably with no load connected.
But I also like to do a test at the other end of the circuit for good measure.
Yes correct the only way to test them at the board is to connect a short piece of cable to them . So general easy to test them at a socket on the circuit .
 
For a first CU change that really is very good - as others have said, it's much neater than a heck of a lot out there done by very experienced electricians. It's really encouraging to see that there are younger tradesmen out there with a really good attitude , well done.
Thank you

Wouldn’t say I was younger though. I’m 43 this year ?

I just chose to have a different career previously before having a complete change of direction.
It helps I suppose that I am OCD. ?
 

Reply to First consumer unit change. in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock