Fused neutral cut-out

Discuss Fused neutral cut-out in the UK Electrical Forum area at ElectriciansForums.net

M

monoloco

Apologies if this isn't the appropriate bit of the forum to post this to, or for any uneducated comments in what follows - straying beyond my elec expertise!

We had our meter changed over to a digital one the other day & the guy who did it spotted we had an old fused neutral cut-out. So Western Power Distribution have been out today wanting to replace it.

I understand enough to appreciate it needs replacing (not that I'd personally be fiddling with wires to come a cropper if the neutral fuse did get blown), but they're saying they need to dig up w nice hole/trench in our (recently tarmaced) driveway to fix it.

Is there a good reason why the service head couldn't safely be replaced without doing that, or is it genuinely unavoidable?

I just want to make sure they're not doing the thing that's easiest/cheapest for them, but not best for us!

Thanks!
 
Only reasons I can think of is to extend the service cable to facilitate the head change, or t repair a section of damaged cable identified on the survey.
Whatever the reason, we can only guess, and as Dillb says only the DNO can answer this.
 
Thanks all.

I'll give them a call and report back.

If it helps to see the cut-out then here's a picture of the offending item!

image.jpg
 
There are ways of doing it BUT to do it safely there isn’t. The DNO’s are obliged to change these heads, at one time they’d modify them.

Post a picture on something like photo bucket and link it to here. If there’s sufficient length on the incomer it can be done, near the floor, forget it.

Do you really appreciate why the neutral shouldn’t be fused?

Pity you only put UK as your location. Some systems were originally DC and converted to AC at a later date. I’m particularly interested in these systems as I’ve lived in two houses that were originally DC. One +ve the other –ve, they were next door to each other.
 
Thanks Tony. Is that photo I've posted visible?

There's only a couple of inches more of the incomer exposed below what you can see there.

As for whether I really appreciate why the neutral shouldn't be fused - as I suggested, this definitely ain't my specialist subject, but I get that the fuse could blow and leave you not realising the circuit's still hot.

Can you explain how it's help to know my location? We're in Gloucestershire - a 1930's house.
 
That cut-out looks very similar to those fitted on 1930's properties,where,on occasion,the DNO or their agents do fit a joint in preference to working on an old unit.

On my own 1937 property,they renewed the head,no problems,in about an hour,but my pal,on the same road,had a joint put in,about a meter from the cut-out.

I inspected his cut-out, previous to this work,and it looked no worse than mine. I think a lot depends on the crew that turn up,and what mood they are in,as when i mentioned this to the lads that did mine,they told me the other crew must "sit down to have a wee"...(actual quote) :jester:
 
It goes without saying that you must not in any way attempt to even open that cutout, let alone do anything else to it.
But for anyone who is interested here's a few pages from the book.
ImageUploadedByTapatalk1429571983.118688.jpg
ImageUploadedByTapatalk1429572028.975680.jpg
And if you are wondering what tools the modern cable jointer might require to practise his trade, here's the list.
ImageUploadedByTapatalk1429572262.906013.jpg
ImageUploadedByTapatalk1429572283.521294.jpg
 
Re cut out change........as said earlier..DNO safe practice.....work on head dead. In order to do that joint hole required. However, as you mentioned new tarmac, ask the DNO to do the joint hole elsewhere. that may well mean doing on the public footpath ( assuming there is one) where your service cable is.
 
Re cut out change........as said earlier..DNO safe practice.....work on head dead. In order to do that joint hole required. However, as you mentioned new tarmac, ask the DNO to do the joint hole elsewhere. that may well mean doing on the public footpath ( assuming there is one) where your service cable is.

sorry I dont follow, how are they going to isolate the head without working live?
 
sorry I dont follow, how are they going to isolate the head without working live?

Hi Dillb, On the face of it, it may sound strange. However it is deemed to be much safer to dig joint hole, cut cable safely, so as to make safe the cutout to work on. Yes, years ago jointers would off worked on the head live. i suppose it safer to work on the separate cores dead as opposed live. Has been that practice for many years. I had to inform customers exactly that whilst I worked for a DNO service alterations. Like the OP's case above....... i would try to avoid sensitive areas like the tarmac.but your governed by the existing service route.
 
Hi Dillb, On the face of it, it may sound strange. However it is deemed to be much safer to dig joint hole, cut cable safely, so as to make safe the cutout to work on. Yes, years ago jointers would off worked on the head live. i suppose it safer to work on the separate cores dead as opposed live. Has been that practice for many years. I had to inform customers exactly that whilst I worked for a DNO service alterations. Like the OP's case above....... i would try to avoid sensitive areas like the tarmac.but your governed by the existing service route.

Yep, they always ditch the cable on my patch too, on cut out changes.
 
I believe WPD jointers need specific authorisation to replace metal clad cut outs live. Not everyone has it and a risk assessment is carried out on each one before it is changed. Risk assessments being subjective and every person being different what one deems to be OK to change live another will want dead (ie service cutting outside)
 
Thanks all!

So it sounds like it depends on their risk appetite & is potentially quite valid for them to say they need to dig outside.

I'll see what options they can suggest for a hole that doesn't wreck our driveway (though unfortunately there's no pavement outside - it's our Tarmac straight to the road).

Should i expect them to have a good record of where the service cable runs?

and on a slightly different note, the house was gutted & renovated in 2011, with all the electrics (on consumer side of the meter) completely replaced. Was it valid for that work to be certified with the fused neutral cut-out left in place? (does that certification only consider consumer-side bits, with meter, service head, etc handled totally independently under DNO regs??)
 
It goes without saying that you must not in any way attempt to even open that cutout, let alone do anything else to it.
But for anyone who is interested here's a few pages from the book.
View attachment 28870
View attachment 28871
And if you are wondering what tools the modern cable jointer might require to practise his trade, here's the list.
View attachment 28872
View attachment 28873

Love it...you would enjoy my book collection! ...only bit that let it down,was the ball "pane" hammer...not seen one of them...:yes:
 
Yes, I noticed that one, it's a bit late to tell the publishers though!

That book is WT Henley's 'practical cable jointing' fifth edition published 1940.

Not got that particular journal,but i do have the appropriate Buck and Hickman catalogue,with most of the equipment listed for sale...i also have a collection of vintage tools,including joint box casts,for bitumen,and even a 9lb lead mould,for casting a "tee" on a water pipe,to save all that wiping!

...Born too late...i fear my lads first phone call,the day after my service...will be to the scrap-man...:smile5:
 
I was surprised to see you can still get CI through and breach joints for 11KV PILC-SWA. When I went to the EMEB I had to take one with me, EMEB didn’t use them but we did. The company still use them to this day.

I’ve never done an 11KV breach joint and I’ll be honest I wouldn’t even attempt one. There’s about 5ft of wiped joints around the lead sleeve. I’d be happy doing a modern breach using a cast resin joint.

I’ve still got my apprentice log books. There’s an entry 11/02/74 for a 11KV termination, 23/07/74 3.3KV through joint and 30/08/74 11KV through joint. A lot of my time was sat in muddy holes.
 

Reply to Fused neutral cut-out in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock