Evening all - got a question that i think i no tje answer but need some assurance!!
Putting a sub main (garage CU) with standard sockets and lights.
Feed to garage CU from suitable MCB in main board that IS RCD protected.
Now........testing ... Most garage CU come with RCD, my understanding is RCD in series a pain so looking for the correct way to test - or is it easier to get a sub main with a 100A main switch no RCD? Thanks
 
Thanks both - problem is the main DB is split load 2xRCD board so all MCBs are RCD protected gggrrrrrr!
i have a mk sentry metal db dual split rcd and just slid the rcds and mcbs up the din rail to make room for an mcb between the main switch and the first rcd. put a short buzz bar to connect it. 20190121_163116.jpg
 
Evening all - got a question that i think i no tje answer but need some assurance!!
Putting a sub main (garage CU) with standard sockets and lights.
Feed to garage CU from suitable MCB in main board that IS RCD protected.
Now........testing ... Most garage CU come with RCD, my understanding is RCD in series a pain so looking for the correct way to test - or is it easier to get a sub main with a 100A main switch no RCD? Thanks
Yes Change to Main Switch
 
How would you record the install? MWC for the main DB to garage DB ( assuming using MCB that is there already and has 6mm cable just re-routing) and EIC for garage DB
 
How would you record the install? MWC for the main DB to garage DB ( assuming using MCB that is there already and has 6mm cable just re-routing) and EIC for garage DB

House CU to garage is “new circuit” and garage DB is a “new CU”, so both require an EIC to be issued and LBC notified.
 

Reply to Garage CU and RCD in series in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock