Currently reading:
Generator sizing help

Discuss Generator sizing help in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
28
Hi all.
I've been out to look at a mates new (to him) air compressor. It's 15kw 3phase star-delta run. He's off grid and currently has a 20kVa Genny running his farm.

This is obviously undersized for starting the compressor, when tried the Genny bogs down and contactors start chattering. He's going to buy another used Genny. He's thinking 30kVa.

Can anyone offer some advice to help me size this correctly?

Thanks
 
Unless you've got an already 'warm' set under load, any sudden inductive inrush is going to cause a genny of any size to splutter. If you're looking at getting a second set my personal preference would be to get something like a 30-40 and fit syncing panels to both so that they can be used asynchronously (take a look at DSE stuff). Also means that at busier times (electrically) there's overhead available. You don't have to run both sets at the same time, you can flip between either or both. Also has the benefit that you can take one offline for maintenance but still have power.
 
To be honest, the set up is less than ideal, he has the generator that is at most used to run individual pieces of workshop equipment, welder, compressor etc, and to top up his off grid battery storage for his house.
The Genny is only started as and when he needs it. Probably rules out the syncing panels.
 

Reply to Generator sizing help in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock