Search the forum,

Discuss Grey area in regs ?? in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
0
Hi All,

What's your thoughts on this. If you have a 2.5mm radial bunched in with a ring main on a 32a breaker then that's a C2 but you can spur off a ring main out in the field no problem...

What's the difference ?
 
A radial circuit usually means more than one point.... whereas a spur is just one point.

The spur can come off a ring at any point, including the OCPD, in your case the 32A.

A radial, in 2.5, would have to come off a 16 or 20A.... serving more than one point.

A spur from the origin has never been a C2, but a radial circuit would be, when serving more than one point.
 
A radial circuit usually means more than one point.... whereas a spur is just one point.

The spur can come off a ring at any point, including the OCPD, in your case the 32A.

A radial, in 2.5, would have to come off a 16 or 20A.... serving more than one point.

A spur from the origin has never been a C2, but a radial circuit would be, when serving more than one point.
Yea i see the thinking, but 1 x local socket bunched into the 32a MCB can't go un-noticed ? Protective device is deemed over-rated surely ?
 
Current carrying capacity of ring final conductors must be at least 20A.

A spur will feed no more than 1 double socket, so is not expected to draw more than 20A (BS1363 double sockets can withstand a steady 20A). It won't overload the cable.

A radial can feed infinite sockets, so it is possible to exceed the current carrying capacity of the 2.5mm cable (max. 27A method C). The cable will be protected if the breaker is rated less than the cable, but a 32A breaker isn't, so it won't.
 
Exactly. The 32A MCB protects 2.5mm against short-circuit, the single point served protects it against overload. Job done.

Ah, you say, the official loading of a double socket might only be 20A but it could be loaded to 26A, even to 40A for some time before the two 13A fuses or the 32A MCB respond. Well, just like the RFC, it works fine in practice because 2.5 clipped to surface can handle 50 amps or more without failure (although it does go a bit soft!)

RFC - triumph of empirical success over theoretical doubt.
 

Reply to Grey area in regs ?? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello, I need to run a mains spur off the existing ring main in a domestic property. To get the double socket to the correct place I have to drill...
Replies
3
Views
275
I would like to reuse a 10mm cable to provide a ring circuit in an area. The cable is currently used for an electric shower, still connected at...
Replies
11
Views
451
Hi, if getting back to the CU is not an option, instead of spurring off a socket via a Sfs putting the rating down to 13a. Could you spur off the...
Replies
43
Views
2K
Hi all, I am at odds on whether RCD protection is required on an SWA of 14 metres, clipped direct under flooring direct from CU to an exterior...
Replies
9
Views
901
We have a room in the house that was the kitchen. That has been relocated to a different area, so the old kitchen has been sold off and the room...
Replies
2
Views
710

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock