Top right hand side of Pic DP MCB with TWECC coming out at the bottom, looks damaged to me where it bends into the enclosure, or do I need to go to Specsavers?I am installing solar to a house and this is there main incoming. I can’t see an Earth anywhere but test ZS across L-N coming out at 0.20. Then with gas bond disconnected is 0.38! But we only have gas bonding. No other earth anywhere. Anyone had this?
View attachment 44800
View attachment 44801
You say Zs across L-N...
What about the true Ze or Zdb?
Could be someone had converted it to TNCS without DNO.
What about a pic of the main earth terminal in the cu? And a wider shot showing all the incoming gear.
Top right hand side of Pic DP MCB with TWECC coming out at the bottom, looks damaged to me where it bends into the enclosure, or do I need to go to Specsavers?
Wassat blue jobby mid righhand of piccy?Sorry zdb is what I ment. Here is a full pic and there is no main earth terminal. The 6’m gas bond goes from db to the gas meter. There are a couple of dbs that there earths go back to this ‘main’ db. But this main db only has gas bond earth in it. Nothing else
View attachment 44802
View attachment 44803
looks like some cowboy has taken a T/E feed from that D/P switch and split the cores.Top right hand side of Pic DP MCB with TWECC coming out at the bottom, looks damaged to me where it bends into the enclosure, or do I need to go to Specsavers?
Yes that’s right which was done by meter fitter. This could be a multitude of problems. But atm I neee to find an earthIt's a burry pic but I think that's a 100A DP isolator with red/black T&E passing through brown/blue shrouds of some sort.
Yes me also, wasn't surelooks like some cowboy has taken a T/E feed from that D/P switch and split the cores.
That’s my new db I’m installing for solar taken the neutral out to drill hole for main tails.Wassat blue jobby mid righhand of piccy?
Can’t see how tho as there is one 6mm earth in db which is gas bondAn earth rod outside direct to CU earthbar?
Can’t see how tho as there is one 6mm earth in db which is gas bond
It’s a old detached house which is a fair few meters away from neighbour. I am stumped atmCould be a much smaller cable to the rod. Readings you are getting would not make me think rod though.
Supp bonding from cpc to pipework that is shared with next door's pipework that is bonded and connected to their PME ?
Top right hand side of Pic DP MCB with TWECC coming out at the bottom, looks damaged to me where it bends into the enclosure, or do I need to go to Specsavers?
It’s a old detached house which is a fair few meters away from neighbour. I am stumped atm
Not that I can see no
Sorry that’s correct yesSo with the gas bond removed there is no other earths connected to the CU earth bar apart from the final circuit earths?
There is no other earthsSurely you can see the whole of the earth bar? Is there another earth or not? Your answer seems unsure so just need to clarify.
As I can’t find an Earth would you suggest earth rod? Although this zs at db reading is so lowOld properties often have earth's from random sockets to the incoming water ....
just tried that and it wouldn’t pick an Earth up from the casingThat is a lead sheathed cable coming in which should be connected to the ISCO sealing chamber and other ISCO boxes.
Inspect and test the cover of the sealing chamber to see if it is connected to the lead sheath and then test it to see if it gives a good Ze.
Just t
just tried that and it wouldn’t pick an Earth up from the casing
DNO coming on a slow boat from China? that lead time is a disgrace.DNO don’t seem to care! They bassicly told me to put it on a TT system. They can send someone out to see if it can be changed to PME but that’s a 5 week waiting time.