Still waiting for that pic....What about a pic of the main earth terminal in the cu.
wayayy too technical as it's way past beer o'clock.A pic of the gubbins in the CU might help!
Yeah whats's apnin OP get a grip will youStill waiting for that pic....
DNO don’t seem to care! They bassicly told me to put it on a TT system. They can send someone out to see if it can be changed to PME but that’s a 5 week waiting time.
Yes explained clear as day she just put me on hold and then went on to say they can send someone out in 5 weeks.Did you explain to them that there’s an unearthed cast iron cutout with open holes in the top exposing live parts?
The TT/PME answer sounds more like the standard response to asking for an earth connection rather than reporting this situation.
Yes but something I’d rather find out for myself. He is well aware but I like to look into these things so I know for future reference etc.Maybe seek the advice of your boss - I see you have trainee access.
If that’s the case how come I can’t get any earth reading off the casing?I've seen it before, inside the cast iron isolators theirs a rewireable fuse, what your seeing is a split supply for another building aswell as yours. Back in the 50's it was also acceptable to use the gas as the earth. The meter fitter wants reporting, but it is upto the electrician to give a earth. is it a rural location?
tell them that you will wait a couple of months if they want .Yes explained clear as day she just put me on hold and then went on to say they can send someone out in 5 weeks.
tell them that you will wait a couple of months if they want .Yes explained clear as day she just put me on hold and then went on to say they can send someone out in 5 weeks.
Yes but something I’d rather find out for myself. He is well aware but I like to look into these things so I know for future reference etc.
If that’s the case how come I can’t get any earth reading off the casing?I've seen it before, inside the cast iron isolators theirs a rewireable fuse, what your seeing is a split supply for another building aswell as yours. Back in the 50's it was also acceptable to use the gas as the earth. The meter fitter wants reporting, but it is upto the electrician to give a earth. is it a rural location?
Anywhere?If that’s the case how come I can’t get any earth reading off the casing?
sorry, off the enclosure? That wont be earthed. The installation wont be earthed full stop. its a TT Job, I would actually report it to the DNO. The cut out fuses inside are normally only 40-60ampIf that’s the case how come I can’t get any earth reading off the casing?
Good call. I agree....DNO. Tell them it's old and there's danger involved.Look I’m an adult learner. I have experience but I have not come across something like this. This is why I have written on here for advice. Now some people are just saying call DNO some are saying just TT it. Surely DNO need to see it and change it as it is so old? Or am I wrong and it’s fine and I just need to supply my own Earth? And TT the whole house?
I am installing solar to a house and this is there main incoming. I can’t see an Earth anywhere but test ZS across L-N coming out at 0.20. Then with gas bond disconnected is 0.38! But we only have gas bonding. No other earth anywhere. Anyone had this?
View attachment 44800
View attachment 44801
Back in the 50's it was also acceptable to use the gas as the earth.
Unless I’m missing something I do t see what the problem is. I’ve come across this situation a few times.
You will of course get a loop impedance reading to neutral as the neutral will be connected to earth at the sub station.
In days of yesteryear the gas could be used as the main earth but since the advent of yellow plastic pipes this is not allowed. Water too was used but stopped for the same reasons.
DNO’s have become increasingly less interested in the earthing set up of a property. Even as recently as 25 years ago it was said that he earthing was the responsibility of the consumer. Unless there are live parts exposed at the DNO’s equipment they won’t bother to treat it as urgent.
Easiest solution is to convert the system to a TT and carry on.