Discuss Help with a 3 phase system!! in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

M

mark da spark

Hi all,

I'm sure this has been asked before and I've had a look on the forum but can't seem to find an answer.

I'm just designing a 9.66kWp system over 3 phases. 3 x 3.22kWp with 3 sunny boy invertors which will keep it under G 83/1. 3 ac and dc isolators next to invertors and I will run 3 SWA's to where the existing consumer units are. There is no space on any of them.

Now my question is what to do next? 3 single phase generation meters or 1 3 phase?
What sort of isolators? 3 double pole or 1 4 pole isolator? What sort of consumer unit/units should I use when i come of each of the phases with emery blocks?

Any help would be much appreicated.

Thank you,
Mark
 
It will be cheaper with one 3 phase inverter such as a Sunny Tripower 8000TL or 10000TL. Then you have just one AC cable to run, one 3 phase meter and your choice of 3 or 4 pole isolator - strictly I believe the 4 pole is only required for TT systems not TN

Regards
Bruce
 
I am an advocate of 3 x single phase inverters but now with the Tripowers from SMA I think I will go down this route now. I have a 9.990kWp in plan and have specked the 10000TL. One three phase way required, One 3ph gen meter and one 4 pole AC isolator.

Might be worth a look.
 
Tripower definately ,very easy to do simple install easy to commision
as for the AC isolator I'm sure you need 4 pole TPN regardless of earthing system for Pv ,on the one I did It was TT but I'm sure I read it either regs or GN7 ,DTI Bipv etc If i find it I'll post it here
 

Reply to Help with a 3 phase system!! in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock