Currently reading:
Help with EICR codes!!

Discuss Help with EICR codes!! in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Reaction score
39
Evening..I'm after a bit of advice coding an EICR I have done today, I don't do an abundance of them so just a bit unsure.

1. 3 sockets spurring of a ring without a fused spur.

2. Evidence that ring cables had been joined behind the DB, the L & N end to ends gave me the results I was looking for but the CPC was 0.01 ohms. I tested at a socket with the 2 legs at the board out and got a correct reading which suggests figure of 8 wiring on the CPC.

3. Socket circuit wired through metal conduit buried in the wall with metal back boxes connected, the earths for the sockets have been taken off the back boxes.

4. Back boxes not earthed on various circuits

5. Incorrect colours used on socket circuit.

Thanks in adavnce.
 
1.
do you mean there are 3 sockets spurred separately off 3 parts of the ring? if so, no code.

2.
is the wiring system to the sockets, singles in metal conduit, if so the live and N will be rings but the cpc may well be the conduit system itself.

3. look at 2.

4. are the back boxes earthed through the accessory? if so no code, although i prefer to see a wire link.

5. what colours?
red / black all is good,
green, pink, white etc. incorrect identification of conductors.
 
1.
do you mean there are 3 sockets spurred separately off 3 parts of the ring? if so, no code.

2.
is the wiring system to the sockets, singles in metal conduit, if so the live and N will be rings but the cpc may well be the conduit system itself.

3. look at 2.

4. are the back boxes earthed through the accessory? if so no code, although i prefer to see a wire link.

5. what colours?
red / black all is good,
green, pink, white etc. incorrect identification of conductors.

1.
do you mean there are 3 sockets spurred separately off 3 parts of the ring? if so, no code.

2.
is the wiring system to the sockets, singles in metal conduit, if so the live and N will be rings but the cpc may well be the conduit system itself.

3. look at 2.

4. are the back boxes earthed through the accessory? if so no code, although i prefer to see a wire link.

5. what colours?
red / black all is good,
green, pink, white etc. incorrect identification of conductors.

is it a flat in a block?
Is it MI?
It's in an office.

No, not MI
 
1.
do you mean there are 3 sockets spurred separately off 3 parts of the ring? if so, no code.

2.
is the wiring system to the sockets, singles in metal conduit, if so the live and N will be rings but the cpc may well be the conduit system itself.

3. look at 2.

4. are the back boxes earthed through the accessory? if so no code, although i prefer to see a wire link.

5. what colours?
red / black all is good,
green, pink, white etc. incorrect identification of conductors.
3 sockets in a line off 1 socket.
 
Without digging out my 15th Ed you could use the yellow and blue for single phase identification but I am 99% sure this only applied to distribution and not final circuits.
What are your Coding thoughts OP.
 
So it's likely that the 2 T+E ends in the DB join L to L and N to N onto singles, but the CPCs connect to the metal conduit,(this is all hidden somewhere) then the CPC is taken off every back box to connect to the socket. Is this acceptable?? Obviously I can't get R1R2 off this so would I take an R2 reading off the furthest socket? The Zs readings I took were all acceptable.
 
Last edited:
It was often misread and should only be applied to distribution circuits not final circuits like you have.
 

Reply to Help with EICR codes!! in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top