Currently reading:
Idiotic Schemes and members

Discuss Idiotic Schemes and members in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
235
Went to a job the other day and found that an NICEIC approved domestic installer employed by a conservatory company had installed a small CU and run a 4mm 3
Core SWA to run some sockets and lighting in the conservatory.

On closer inspection he’d split the tails with Henley block to feed to new CU. He’d then installed a flex gland for the SWA (no popper gland) but worst of all, he’d installed a BS61008 32a 30ma RCD for protection. No overcurrent protection at all!

We decided to inform the house owner. She said she’d get on to the conservatory company. She checked the certificate and found that he’d left the overcurrent box blank.

After she’d contacted the conservatory company, I get a call today from the house owner saying that the ‘sparks’ had shown up unannounced and was very aggressive. He didn’t want to talk to me in the phone. She said he went to something in the conservatory and announced, ‘look, it is earthed!’ She proceeded to tell him that the problem was with the breaker and what was on the certificate. When he was shown the certificate (which was about 4 years old) he snatched it and filled in the blank box with the numbers ‘61008’.

Now tell me, why oh why oh why are the NICEIC letting people in like this? When we were admitted into the NIC, I for one was so proud to be a member. Since the advent of the other schemes, this trade has gone to sh*t! I feel so sorry for this lady.

It seems that the NIC maybe more interested in revenue than having fully qualified professional electricians as members and could it be that this is because I all the other schemes are too!?

You’d think they’d all know by now that price based competition lowers standards whereas service based competition raises standards!
 
Why do you think that other schemes are to blame for the poor standards found within the ranks of the NICEIC domestic installer scheme ?
For years and years the NICEIC let in applicants with minimal qualifications, the lowest of all schemes. They actively collude with Electrical Trainee training centres to churn through revenue supplying applicants.

Any cheapening of the reputation the NICEIC once had is their own making.

Give them a call about the conduct of this particular installer and see how much of a ---- they give.
 
I did a recent post,where i was called to give an opinion on a recently fitted domestic CU. That too,was installed by a member of a well known scheme...can't say which one,but it's the same one...:rolleyes:

Obviously no testing done previous to ripping original one out,must have realised issue too late,and hey presto...all lights and upstairs sockets are on a 6A MCB...which the hoover sorts out 4 times out of 5.

Feedback from stunt-fitter,was "yeah,can be a problem,them old properties..."

Is it the worst i've seen? ... Not by a long chalk...:(
 
Why do you think that other schemes are to blame for the poor standards found within the ranks of the NICEIC domestic installer scheme ?
For years and years the NICEIC let in applicants with minimal qualifications, the lowest of all schemes. They actively collude with Electrical Trainee training centres to churn through revenue supplying applicants.

Any cheapening of the reputation the NICEIC once had is their own making.

Give them a call about the conduct of this particular installer and see how much of a **** they give.
I don't think he's saying the other schemes are to blame. He seems to be castigating them.
This all came into being with the government instigated 'changing of the goalposts'.
Your 'years and years' then began.
As a result, the schemes came along, creating today's farcical, money making, disgrace.
'NICEIC approved domestic installer', throws me a bit, though.
 
Last edited:
Went to a job the other day and found that an NICEIC approved domestic installer employed by a conservatory company had installed a small CU and run a 4mm 3
Core SWA to run some sockets and lighting in the conservatory.

On closer inspection he’d split the tails with Henley block to feed to new CU. He’d then installed a flex gland for the SWA (no popper gland) but worst of all, he’d installed a BS61008 32a 30ma RCD for protection. No overcurrent protection at all!

We decided to inform the house owner. She said she’d get on to the conservatory company. She checked the certificate and found that he’d left the overcurrent box blank.

After she’d contacted the conservatory company, I get a call today from the house owner saying that the ‘sparks’ had shown up unannounced and was very aggressive. He didn’t want to talk to me in the phone. She said he went to something in the conservatory and announced, ‘look, it is earthed!’ She proceeded to tell him that the problem was with the breaker and what was on the certificate. When he was shown the certificate (which was about 4 years old) he snatched it and filled in the blank box with the numbers ‘61008’.

Now tell me, why oh why oh why are the NICEIC letting people in like this? When we were admitted into the NIC, I for one was so proud to be a member. Since the advent of the other schemes, this trade has gone to sh*t! I feel so sorry for this lady.

It seems that the NIC maybe more interested in revenue than having fully qualified professional electricians as members and could it be that this is because I all the other schemes are too!?

You’d think they’d all know by now that price based competition lowers standards whereas service based competition raises standards!
One word Marky Money
Went to a job the other day and found that an NICEIC approved domestic installer employed by a conservatory company had installed a small CU and run a 4mm 3
Core SWA to run some sockets and lighting in the conservatory.

On closer inspection he’d split the tails with Henley block to feed to new CU. He’d then installed a flex gland for the SWA (no popper gland) but worst of all, he’d installed a BS61008 32a 30ma RCD for protection. No overcurrent protection at all!

We decided to inform the house owner. She said she’d get on to the conservatory company. She checked the certificate and found that he’d left the overcurrent box blank.

After she’d contacted the conservatory company, I get a call today from the house owner saying that the ‘sparks’ had shown up unannounced and was very aggressive. He didn’t want to talk to me in the phone. She said he went to something in the conservatory and announced, ‘look, it is earthed!’ She proceeded to tell him that the problem was with the breaker and what was on the certificate. When he was shown the certificate (which was about 4 years old) he snatched it and filled in the blank box with the numbers ‘61008’.

Now tell me, why oh why oh why are the NICEIC letting people in like this? When we were admitted into the NIC, I for one was so proud to be a member. Since the advent of the other schemes, this trade has gone to sh*t! I feel so sorry for this lady.

It seems that the NIC maybe more interested in revenue than having fully qualified professional electricians as members and could it be that this is because I all the other schemes are too!?

You’d think they’d all know by now that price based competition lowers standards whereas service based competition raises standards!
One word Marky (MONEY)
 
If you ask the schemes about this sort of stuff (I have at Elex) they say its not within their remit to investigate ............... go figure .......... makes you wonder why it worth the hassle.........
You could try emailing EMMA CLANCY at certsure, but in hindsight She will do SFA.
 
You could try emailing EMMA CLANCY at certsure, but in hindsight She will do SFA.

One of my customers had a problem with one of their members ..... all the NICEIC said was get them back ........... which she didn't want to do ........... so she paid me to investigate and passed the NICEIC member my costs and told them to come back .......... which they did, thinking they were going to get the roofing work too (they were general builders) .............. when they finally turned up ......... the roof had been done by others and 2 of them spent 1 day fixing the issue.

funny

and when I was there last week I did test to confirm the issue had been fixed .......... the contractor didn't provide a cert .....

Surely these organisations must read these comments?
 
One of my customers had a problem with one of their members ..... all the NICEIC said was get them back ........... which she didn't want to do ........... so she paid me to investigate and passed the NICEIC member my costs and told them to come back .......... which they did, thinking they were going to get the roofing work too (they were general builders) .............. when they finally turned up ......... the roof had been done by others and 2 of them spent 1 day fixing the issue.

funny

and when I was there last week I did test to confirm the issue had been fixed .......... the contractor didn't provide a cert .....

Surely these organisations must read these comments?
They have thick skins Mate, thick skins and big wallets, they don't care about anything but making Money, despite what was said at the Big Committee meeting held a few years back, it's a business not a service, and what do businesses thrive on? Profit (Money), sorry to go on (probably get some "old" icons, but this isn't a new thing is it?
 
One of my customers had a problem with one of their members ..... all the NICEIC said was get them back ........... which she didn't want to do ........... so she paid me to investigate and passed the NICEIC member my costs and told them to come back .......... which they did, thinking they were going to get the roofing work too (they were general builders) .............. when they finally turned up ......... the roof had been done by others and 2 of them spent 1 day fixing the issue.

funny

and when I was there last week I did test to confirm the issue had been fixed .......... the contractor didn't provide a cert .....

Surely these organisations must read these comments?
They have thick skins Mate, thick skins and big wallets, they don't care about anything but making Money, despite what was said at the Big Committee meeting held a few years back, it's a business not a service, and what do businesses thrive on? Profit (Money), sorry to go on (probably get some "old" icons, but this isn't a new thing is it? gather lots of evidence and send it to the Chair of that Committee meeting, can't recall his name, but someone will know, failing that send the evidence to you Local MP recorded delivery of course.
 
Someone posted about Napits recent proposal, which sounded relatively reasonable, apart it being restricted to registered business.

https://www.parliament.uk/documents...t-P-and-the-Independent-Review-20-June-18.pdf

And being a member of a scheme of course. :)


That’s not a bad start. I would go further though.

The five week wonder schemes for Part P should be banned, full stop!

This is because a requirement for entitlement into a scheme to enable someone to self certify their electrical work should be that you are a qualified electrician to start with!!!!!

Just because you have a regs course doesn’t mean you are capable of safely wiring a kitchen (where most of the electrical load is) or a bathroom where a lot of the danger is, or a garden where a lot of people get hurt. If this were the case, what is the point of the three years or more that we as qualified professional electricians did?

There should be much much more of a recognition of the C&G or NVQ qualifications that one does to become a qualified electrician and this should be taken into account when applying for the self cert schemes, and any other scheme including the ECS.

The ECS is another bloody joke. They don’t even recognise a C&G now and yet they are giving gold cards to guys who have only just qualified with an NVQ and no site experience. Most wouldn’t even know where to put their name in an EIC or EICR. The excuse is that the C&G is not now current qualification for being an electrician! Go figure!?

Another big question is that why does Part P only apply to domestic properties????
If it’s needed at all (which I don’t believe it is as we have enough legislation in exams and qualifications anyway) it should be applied across the board. Electrical is electrical is electrical!
Why is there a distinction between domestic and any other kind of electrical work at all? If installed incorrectly it kills, end of!

In my opinion Part P is a sticking plaster that was made of tissue, didn’t really have any adhesive and is now beginning to peal off. All qualified sparks have one thing in common; we are all qualified! We did the appropriate qualifications to become professional electricians.
Surely these qualifications alone should be the absolute basis, starting point or foundation for any Part P or similar scheme!

We, as qualified electricians, have spent three or more years training for this trade, only to be upstaged or downgraded by someone who has none of the necessary qualifications but who has done a five week course. They are then admitted into a self cert body and are not even qualified electricians. They can then install electrical equipment and circuits, certify and even sign off the work under law as being safe!!!!!

This is a crazy situation and needs to be changed immediately.
 
The idea also was supposed to control the work of kitchen and bathroom fitters. They do the Electrical Trainee or whatever the course is called and then suddenly Kevin is an electrician changing consumer units etc whereas once he was doing small alterations. For them should have been graded limited scope.
 
The idea also was supposed to control the work of kitchen and bathroom fitters. They do the Electrical Trainee or whatever the course is called and then suddenly Kevin is an electrician changing consumer units etc whereas once he was doing small alterations. For them should have been graded limited scope.

I have never understood why kitchens were removed from part p - kitchen fitters are some of the worse offenders for ignoring BS 7671 imho
 

Reply to Idiotic Schemes and members in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock