OP
pauldreed
What do you want to know? I have covered the basic principles in post #16 of how it works.Hi can you tell me more about your device
Discuss Immersion Heater - PV electricity in the Central Heating Systems area at ElectriciansForums.net
What do you want to know? I have covered the basic principles in post #16 of how it works.Hi can you tell me more about your device
I use current transformers, one on the power feed from the invertor (which measures the power being generated) and a second on the ring main power feed (to measure the power being used in the home).Hi yes you described how it worked but can you let me know what you have used to monitor the system to enable it to switch the immersion on and off at the appropriate time. Thanks.
Op amp, as I couldn't find an all inclusive module.Hi Pauldreed
Are you using an op amp to do the comparison to then drive a relay or do you have an all in one module?
Thanks
Yes, hysterisis has been a problem, and I had to modify my circuit after a few weeks as the relay couldn't cope with the rapid switching.
I have never used, or know anything about micro-controllers, so I can't comment on your suggestion, but good luck.
I was educated in electronics 30 years ago, so microcontrollers have not figured until now!Thanks Paul. Microcontroller are really very simple once you get the hang of them and so flexible for this sort if thing and limited only by imagination and a couple of pounds gets something capable of automating and running most thing in a house. They are probably simpler than other ICs and changes are a simple reprogram rather than changing components. I use them a lot for sports based control systems.
Once I have the pv system installed I'll potter around with something to sort out the immersion heater etc.
If you think you might want to know a bit more by all means drop me a note - it might be a simple relaiable solution for optomising pv.
I was educated in electronics 30 years ago, so microcontrollers have not figured until now!
Presumably, you need a programmer - to interface to a PC, which in turn writes the instructions to a chip.
The chip with minimum support components would then retain the instructions and operate independently to the programmer?
Reply to Immersion Heater - PV electricity in the Central Heating Systems area at ElectriciansForums.net
We get it, advertisements are annoying!
Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.