- Reaction score
- 2,439
Seems to be my month for finding odd bodges by supposed professionals.
Installing an external socket in a shed today at a park home (non-mobile home) and find this label on the consumer unit:
and this behind the door:
It looks like the CU was installed at the factory and then shipped with the house to site, where someone installed it on a TT and left it like it.
A more recent electrician apparently put a bigger earth rod in (8 feet rather than the 2 feet - Ze of 22 Ohm so fairly good as earth rods go) and the gas people discovered a 'reverse polarity' that was fixed.
But (according to the client at least) at no point did anyone tell him that none of the lighting, Central Heating or Oven circuits were protected by anything other than MCBs with a Zs that would certainly not meet any disconnection times.
The label is just plain confusing though. I know in the 16th there was a regulation that socket outlets needed RCD protection, and that's fine. But it ignores the fact that I've never seen a TT system where some sort of upfront RCD wasn't required for all other circuits to meet disconnection requirements. I'd have expected them to have fitted an S type RCD as the main switch at least, but no doubt this saved them some pennies.
I've also never seen a modern RCD described as an Earth Leakage Circuit Breaker - I thought that only applied to the old voltage ones which were considered obselete in the 80s.
Currently putting something in writing to the client so they can brandish it to the site owner, who is apparently not known for his adherence to regulations, and will quote for a new board.
Anyone seen a label like this before?
I'm thinking I'll quote for a Fusebox RCBO board with SPD as they seem good at the price. Though even a Screwfix special dual RCD would be an improvement!
Installing an external socket in a shed today at a park home (non-mobile home) and find this label on the consumer unit:
and this behind the door:
It looks like the CU was installed at the factory and then shipped with the house to site, where someone installed it on a TT and left it like it.
A more recent electrician apparently put a bigger earth rod in (8 feet rather than the 2 feet - Ze of 22 Ohm so fairly good as earth rods go) and the gas people discovered a 'reverse polarity' that was fixed.
But (according to the client at least) at no point did anyone tell him that none of the lighting, Central Heating or Oven circuits were protected by anything other than MCBs with a Zs that would certainly not meet any disconnection times.
The label is just plain confusing though. I know in the 16th there was a regulation that socket outlets needed RCD protection, and that's fine. But it ignores the fact that I've never seen a TT system where some sort of upfront RCD wasn't required for all other circuits to meet disconnection requirements. I'd have expected them to have fitted an S type RCD as the main switch at least, but no doubt this saved them some pennies.
I've also never seen a modern RCD described as an Earth Leakage Circuit Breaker - I thought that only applied to the old voltage ones which were considered obselete in the 80s.
Currently putting something in writing to the client so they can brandish it to the site owner, who is apparently not known for his adherence to regulations, and will quote for a new board.
Anyone seen a label like this before?
I'm thinking I'll quote for a Fusebox RCBO board with SPD as they seem good at the price. Though even a Screwfix special dual RCD would be an improvement!