Kitchen sockets keep tripping.

Discuss Kitchen sockets keep tripping. in the UK Electrical Forum area at ElectriciansForums.net

Phil2203

DIY
Reaction score
1
Hi all, hope everyone has had a nice Christmas. At some point this morning the kitchen sockets tripped and its had me up the wall, literally.

It has happened in the past but I just flip the breaker back up and it's been fine. Not today. Flip it up, few seconds later it trips the downstairs rcd. Flip the kitchen fuse off then all power downstairs is fine.

I've had all the sockets off looking for damaged/loose wires but all seem sound.

Theres nothing unusual on the circuit, 4 sockets, fridge freezer, dishwasher etc...

I dont think its overloading, yesterday I had the microwave, steamer, kettle, extractor fan on all at the same time and was fine.

Any ideas guys???? Thanks
 
As above , unplug / disconnect absolutely everything from the circuit and chances are it will reset & hold in...

very rarely will a fault on the internal wiring develope out of the blue
 
Hi all, hope everyone has had a nice Christmas. At some point this morning the kitchen sockets tripped and its had me up the wall, literally.

It has happened in the past but I just flip the breaker back up and it's been fine. Not today. Flip it up, few seconds later it trips the downstairs rcd. Flip the kitchen fuse off then all power downstairs is fine.

I've had all the sockets off looking for damaged/loose wires but all seem sound.

Theres nothing unusual on the circuit, 4 sockets, fridge freezer, dishwasher etc...

I dont think its overloading, yesterday I had the microwave, steamer, kettle, extractor fan on all at the same time and was fine.

Any ideas guys???? Thanks
What is the device that is "tripping RCD or MCB "
 
Does it coincide with activity?

Pans/kettle boiling.

One thing I've seen is kettles/pans boiling then steam condensing, especially at this time of year on external walls, and running down tiles and into sockets and tripping RCDs.
 
Sounds like an appliance fault to me, likely getting worse over time. Only seen the odd occasion where a fault has developed on a circuit over time, usually from poor install (slightly damaged/ trapped cable etc...).

Are you 100% sure you fully disconnected everything on that circuit?
 
Does it coincide with activity?

Pans/kettle boiling.

One thing I've seen is kettles/pans boiling then steam condensing, especially at this time of year on external walls, and running down tiles and into sockets and tripping RCDs.
Nah not down to activity, it was all go yesterday and was fine. Boiled a kettle once today and it went off an hour or so later
 
RCD. The downstairs circuits are all on the same rcd. Keeps tripping if I try to flip it up, turn the kitchen off and ilts fine
Something on your RFC is causing tripping try unplugging things and gradually turn them back on till the RCD trips ergo there is your problem
 
if appliances are on a FCU and the FCU is only single pole switcthing, could be a N-E fault on an appliance.
 
AFAIK all BS1363 FCUs are DP although that doesn't stop someone making up SP arrangements using grid parts.
 

Reply to Kitchen sockets keep tripping. in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock