Currently reading:
L & N Volts

Discuss L & N Volts in the Australia area at ElectriciansForums.net

the pict

-
Mentor
Reaction score
247
I was round at my local changing some busted kitchen sockets and I thought I'd give them a quick Zs PSC PFC check
however on one I was reading 240 V L N and 67V N E the meter would not do a PFC and the PSC was 660A with a Zs of 45 Ohms which is within range more investigation is needed obviously so wheres the N E volts coming from? looks like I will be down the pub a lot this week and I bet the good lady wont mind a bit :26:
Pict
 
what voltage did you measure L-E ? if thats 240V then you've got a poor N connection somewhere. Zs of 45ohms, TT?
 
biggest problem is after imbibing of a few. the red wire goes somewhere in a hole i can' t shee. the black lid thing ish shurplush to rekwi, requi, riqou, needs, ish dropshed the blurry shcrews in the shellar, bugger it , gish another pint.
 
I have not yey measured Ze I think this is going to more of a job than I first thought, I have been back round to have a proper look, the whole place is 3 phase with 7 DB's at some time there have been RCD's spliced into the supply for 3 boards 2 of which do not respond to the test button, one old cast iron DB has the fuses in the neutrals, I kid you not, 3 of the circuits are copper sheathed going into about 6 inches of render/plaster god knows what they serve or used to serve 2 boards on the upper floors have RCD's of the same rating as the incomer RCD's if you know what I mean, some fuses 3036 are wired with bits from a coat hanger ? but yes the Neutrls look like an issue Oh and theres a DB in the cellar with it's own running water
Pict
 
First thing you should do is check the Ze to the supply arrangements TNCS TT or TNS ,no point doing a Zs if the ze is incorrect or a fault is apparent , by what you have said i think a PIR would be benificial
 

Reply to L & N Volts in the Australia area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top