Search the forum,

Discuss Lighting circuits not protected by RCD in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

C

chloebear

Just carried out an inspection on a domestic property - there is RCD protection on the sockets, water heater & Garage supply but no RCD protection on the lighting circuits & cooker. Just wondering what code to attribute to this - thinking code 4??
 
correct, if it was fitted prior to 17th
 
The age of it's installation is irrelevant as code 4's apply to the latest edition of BS7671.

What is required to decide if these are code 4's is more evidence as to why the code is necessary.
 
I hate to be pedantic here but we test all installations against the current edition of BS7671 regardless of the installation date.
my comment was to say code 4 the lack of RCD on lighting as non=compliant with current regs. assuming installation was done to 16th.
 
Not pedantic - all installations are, or I hope are, tested to the latest edition of the reg's: the original question was relating to gaining an opinion as to if a code 4 was acceptable owing to the fact that the installation was pre 17th edition - if all non conformaties to the 17th were listed as code 1 or 2 and that goes for every further edition to the reg's then it just becomes a free for all for changing every CU in sight regardless of the functionality etc, which in my very humble opinion is not the way to go.
 
The age of it's installation is irrelevant as code 4's apply to the latest edition of BS7671.

What is required to decide if these are code 4's is more evidence as to why the code is necessary.

With a bit of luck the new admendment will do away with that code 4 and we will only have the 3 codes. Though I agree with that I'm not overly happy about the proposed new "Electrical Installation Condition Report". The IET have proposed a lot more paperwork with the inspection schedules and a "Main Intake and Associated circuits" schedule as well. seems that it would encourage the less scrupulous to fabricate rather than do a thorough test
 
If it's cables are run through walls without adequate mechanical protection i.e. to switches surely it's code 2 if there's no RCD and the conditions of reg 522.6.6/OSG 7.3.2 aren't met
 

Reply to Lighting circuits not protected by RCD in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Question is does this DB really need RCD protection as there are only internal lights and sockets supplying this large building that used to be a...
Replies
13
Views
603
As I've mainly done site work and moved into domestic recently, I'm a bit rusty on stuff like this, but if I'm adding a loft PIV unit to an...
Replies
1
Views
707
So I'm getting various responses to this depending on how things are interpreted. Here's a scenario: Assume property is a tenanted property...
Replies
25
Views
2K
I'm interested how you would all approach this one. A 3 phase distribution board on a caravan site, under lock and key. Only warden and manager...
Replies
20
Views
781
hi all come across a new build commercial office where radial circuits feeding electrak power track was protected by 32A RCBO at dist board and...
Replies
15
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock