Currently reading:
Lighting contactor wiring

Discuss Lighting contactor wiring in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
6
I've not had to do a contactor before and just want to check the wiring of it.
It's a 2 pole contactor with a1/a2 and 1234

Am I right in thinking that
A1 = perm live
A2= neutral
1= live to light
2= switched live
Not really sure on 3 and 4

Thanks for any advice
 
A1 and A2 are switched live and neutral That you use for opening or closing the contactor. As for 1,2,3,4 It all depends on which brand of contactor it is as to where they are and what they do but generall if you apply power to a1 and a2 you will be able to use your tester to find out which terminals are linked
 
I'm using it for led strips in a kitchen there's a lots of them and the inrush current trips the mcb and I've been suggested to use the contactor to solve it.

So reading it I don't need to use 3/4
A1= switched live
A2 = neutral
1= perm live
2= live to light
 
All the info should be on the contactor itself including a wiring diagram, coil voltage, no/nc operations.

If you are not sure to how to wire it then you are probably unsure of how it functions. You should research this so you understand it fully.
 
A1 and A2 are switched live and neutral That you use for opening or closing the contactor. As for 1,2,3,4 It all depends on which brand of contactor it is as to where they are and what they do but generall if you apply power to a1 and a2 you will be able to use your tester to find out which terminals are linked
Contactor terminal numbering is normally universal, 1 switches 2, 3 to 4, 5 to 6 etc..
 
I think they will need to be separated to help the reduction in inrush
Use the switched live to feed the contactor coil and one half of the lights and use a permanent live to feed the other half via the switching contacts of the contactor
 
You may find your switch gets damaged over time though. As has been said a current limiter prior to the switch is the more conventional method of dealing with inrush currents. Contactors, relays and switches are all in line of the inrush and will suffer over time. I hope with the C curve MCB you have taken account of the ADS and max Zs that it meets required disconnection times? There is much evidence of fusing and meltdown of contactor, relays and switches in such circuits.
 
I’m am at the property now and have put a c10 mcb in and all seems good have tried them over 50 times and no tripping
upload_2017-11-21_16-31-31.png
 

Reply to Lighting contactor wiring in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top