2 X 6KW fryer = 2 X 6kw fryer = 2 appliances otherwise it would be 1 X 12KW fryer.
You need to take a chill pill, its hard enough deciphering half this stuff without you adding to it

I assume from the fact the OP has seen the spec for the appliance and is designing it as a single supply that a 2x6kW fryer is a single appliance comprising of 2 fryers, each rated at 6kW.

The language in the OP is quite clear "A circuit for A 2x6kW fryer" if it was indeed 2 appliances the OP would use the plurals, "circuits for 2x6kW fryers"
 
That still doesn't explain why you've selected a 32A OCPD for a 17.3A load when 20A would be the more logical choice?
32A would be my preference, the circuit is 15m long so EFLI not going to be an issue here.
No point loading up a 20A TP MCB, he's also stated that the board and mcbs are obsolete and that he had a 32A MCB. Ccc also not an issue after correction factors applied.
 
For what it's worth I did a 3 Phase oven and calculated 2.5 and the manufacturer insisted they always use 4mm. Maybe the manufacturer of the fryers might have some input? I suppose as it is a cafe they do tend to run their appliances at full tilt for much of the day so yeh belt and braces approach.
 
That still doesn't explain why you've selected a 32A OCPD for a 17.3A load when 20A would be the more logical choice?
I agree with you Dave sparks, my apologies I'm not fully up to speed with calcs as being honest I haven't done any in about 20yrs, as all large scale jobs I worked on had designers, so excuse my ignorance. Initially I had drawn up calcs for a 20A breaker but was advised by a designer to up it to 32 A and use a 2 in 1 socket, photo attached15957992659911222419678493902853.jpg. Would you mind me asking for your personal opinion please
 
I assume from the fact the OP has seen the spec for the appliance and is designing it as a single supply that a 2x6kW fryer is a single appliance comprising of 2 fryers, each rated at 6kW.

The language in the OP is quite clear "A circuit for A 2x6kW fryer" if it was indeed 2 appliances the OP would use the plurals, "circuits for 2x6kW fryers"
I will bow to the forums use of english, i could equally have assumed the OP missed off the S but struggling with why it would be described as 2 X 6KW and not 1 X 12KW, so i had assumed he only had one cct, hey ho
 
I agree with you Dave sparks, my apologies I'm not fully up to speed with calcs as being honest I haven't done any in about 20yrs, as all large scale jobs I worked on had designers, so excuse my ignorance. Initially I had drawn up calcs for a 20A breaker but was advised by a designer to up it to 32 A and use a 2 in 1 socket, photo attachedView attachment 59723. Would you mind me asking for your personal opinion please

Nothing wrong with a 32A OCPD lad, cable Ccc OK, EFLI likely to be well under the max.
If this is going to running for 12 - 15 hours a day, a 32A MCB will operate at a cooler temp than a 20A MCB in this environment.

Your the designer at the end of the day!
 
I will bow to the forums use of english, i could equally have assumed the OP missed off the S but struggling with why it would be described as 2 X 6KW and not 1 X 12KW, so i had assumed he only had one cct, hey ho

For me that is a perfectly normal way to describe the power rating of something, I see a lot of equipment with ratings like that. For example I install stage lighting dimmers described as 12x2.4kW or 24x2.4kW, these are single pieces of equipment which have 12 or 24 channels of 2.4kW dimmers.

Or a 2x13A socket is not 2 seperate items, it's a single plate with 2 bs1363 sockets on it, it's also not a 26A socket.
 
2 X 6KW fryer = 2 X 6kw fryer = 2 appliances otherwise it would be 1 X 12KW fryer.
You need to take a chill pill, its hard enough deciphering half this stuff without you adding to it
Sorry plugs and sparks, I wasn't clear in my description, this is a twin fryer but 1 single piece of equipment, that is why I asked for you to explain, no offence intended. These fryers can be used individually or both together and come in both single and a 3ph option.
 
For me that is a perfectly normal way to describe the power rating of something, I see a lot of equipment with ratings like that. For example I install stage lighting dimmers described as 12x2.4kW or 24x2.4kW, these are single pieces of equipment which have 12 or 24 channels of 2.4kW dimmers.

Or a 2x13A socket is not 2 seperate items, it's a single plate with 2 bs1363 sockets on it, it's also not a 26A socket.
Interesting.. I would never describe a double socket as a 2 X13A socket, that would be 2 X single gang sockets. It would be interesting when the fryer shows up what the rating plate says.... please OP take a pic.... it might make my day ( or not) lol
 

Reply to Looking to install a 3ph supply for 2 x 6kW fryer in a commercial kitchen. in the Commercial Electrical Advice area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock