To measure an earth rod, you need a 3 or 4 lead tester, depending on the make, one lead is attached to the rod, then the other leads are attached to twigs, er sorry probes which are then placed in the ground at given distances from the rod. Any connection's to installation would need to be disconnected.
 
We can use an EFLI tester, this gives enough accuracy on the side of caution to measure this.

Granted you may need a proper tester for the installations of generators and the like on some larger industrial sites, you can also use stakeless testers now as well.
 
15 mins to check your rods? Why?

I suppose you want your ra values.

You would have checked them before? Why don't you just plug in a metre into a socket and loop it, then do your rcd tests?

2 mins max. Which leaves you 13 mins dig your metre out.


Maybe in you're world everything is prepared and all you do is push the button, doesn't quite work like that in the real world though!!


Insanity: doing the same thing over and over again and expecting different results.
Albert Einstein



Which all goes to show, just how little you know about TT systems!!
To measure an earth rod, you need a 3 or 4 lead tester, depending on the make, one lead is attached to the rod, then the other leads are attached to twigs, er sorry probes which are then placed in the ground at given distances from the rod. Any connection's to installation would need to be disconnected.


And is exactly the method i use as i have an open field to the back of my property, so i have the distance to obtain accurate measurements... I'd like to see you hook that little lot up and conduct the tests in 3 mins!! ...lol!!


Engineer54 a "working" earth what the hell is that? Us electricians call it a stable or un stable earth.

Stability is an important factor, but a working TT system (earth) is one that is as near TN values as you can possibly get, and not one, that you'd probably be happy with, by following the BGB!!


I think most Engineers, especially those that are site based HAVE to live in the real world, and probably more so than the average jobbing electrician. Responsibility comes with a price when you get it Wrong, as even some small errors, can end up costing the client or the contractor (or both)some pretty serious money!!
 
I think a serious waste of money is trying to acheive TN values on a TT system.

Depends entirely on the site, it may be well be cost effective and desirable on large projects to achieve TN values from a TT system, the cost savings of not needing RCDs alone would make it worth while (not talking about final circuits here), using TNC-S and PMEing such a large project may also have massive cost implications, and may not be an option based on cost grounds, this could be down to the size of the bonding conductors, or it may simply be not allowed at all for one reason or another, likewise TN-S may also have huge costs attached.

This is where E54 is perfectly correct, but I also tend to fit in the other camp where domestic is concerned, that is I try to get it as low as is reasonably practicable, but see little point in over engineering it past say two rods driven deeply, if I can get it reasonably low (below tens of ohms) and stable I am usually happy.
 
Last edited:

Reply to Max Ze for TT system in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock