The OP asks about a particular cable, I wonder if this is significant? The IR for the cable itself will be as per the manufacturer's info and will be inversely propotional to length, given in the form x megohm.km i.e. divide the figure by the length in km to get minimum value in megohms. But for a circuit, including the fittings at both ends and an unspecified length of the cable, as stated above.
 
Last edited:
The OP has not stated whether or not this is in an industrial setting,or how old the cable is. Some types of cable,in this instance,would have a calculated IR value far below what is stated in any "modern" regs book...and if a previously redundant cable was being brought back into service,monitoring would ensue,to check for a probable rise in IR value.

...1Meg...i hang awake at night,dreaming of 1Meg...:wacko:
 
Good evening gents.

Thanks for the helpful advice where given. Warm and dry now. Sorry for the lack of info. It was motorway spec cable. 150Ohms/L is the minimum. Was not thinking straight due to the frost bite setting in but knew it was there abouts.

Think sometimes to often when a question is asked on here the answer is look at the regs. Sometimes you need a little help in a shtt situation.

Cheers
 
1 meg is a wonderful 'one size fits all' solution which makes no allowance for any real world factors which may apply to older cables or equipment.
It seems a bit ridiculous to me that a brand new installation only needs to meet this 1meg requirement the same as any old installation is judged by the same standard.
There is an old formula which can be used to relate the minimum value to the individual situation. The insulation resistance should be sufficient to ensure that the earth leakage current is no more than 1/10000th of flc
 
Good evening gents.

Thanks for the helpful advice where given. Warm and dry now. Sorry for the lack of info. It was motorway spec cable. 150Ohms/L is the minimum. Was not thinking straight due to the frost bite setting in but knew it was there abouts.

Think sometimes to often when a question is asked on here the answer is look at the regs. Sometimes you need a little help in a shtt situation.

Cheers

Hi bud,this would have been easier,if we knew the situation and type of cable.

Where has the "1500hms/L" come from? :smiley2: ...or "150 Ohms/L" even?
 
Last edited:
The original question asked what the minimum IR value for a 230v cable is as a regs book wasn't to hand, that implies the OP required the minimum value stated in bs 7671...which is 1 megohm!

It's no longer clear exactly what the OP was asking but there's an important difference between the minimum acceptable IR for 70mm² cable and the IR for a circuit using that cable. 1 metre of 70mm² would be considered faulty and rejected if it could only achieve 1MΩ, but wire it between a fuse-switch and a busbar chamber and test it on a damp day and 1MΩ might be realistic. OTOH a 600m run of cable might not be so bad at 1MΩ so when you are looking at larger cables and longer runs you can't just say 1MΩ is the limit and that's that.

Hence the figure in MΩ.km (sometimes misquoted as MΩ/km which is a nonsense) that manufacturers give for each size and type of cable, or they refer to the one in the BS for that cable. If the '150 ohms/l' is supposed to say megohms then it makes sense to me.
 
Spanner in the works. 1500 Ohms or 1.5MOhms is the minimum per kilometer / by the Length is the minimum for motorway spec power cable. Typo after one of those days where you are glad to put behind you. Thanks all the same.
 
Last edited by a moderator:

Reply to Minimum IR in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top