Hi all,
Was hoping to get some light shed on the particular cause to an issue we had last night.

Was woke at 2 in the morning by my partner saying none of the sockets were working. I went to the CU and the sockets MCB had tripped as well as the RCD.

Flicked them both back on, but the sockets ring remained unpowered, all of them, even with the MCB still on. Couldnt be bothered to try and fix at 2am, so switched it off and went to bed.

Next morning, still not working. So i removed the cover to see if there was a loose connection. Upon tightening up the connections, the sockets ring was fine, but the kitchen sockets were loose on the outgoing and the incoming for the shower was not even close to being tightened up.

I cant see how these would affect the sockets tripping on another MCB though so am inclined to write it off as a coincidence.

Having turned the sockets mcb off and on a few times, theyre working again, so am lead to believe we are looking at a faulty MCB?

As for the MCB and RCD tripping at the same time, is that an indicator of a short to earth?

Cheers in advance for any advice

Joe
 
Sometimes a bad connection can cause a surge as it reconnects on to a load which might just trip things. But hopefully you have checked ALL of the terminals for tightness now and it might be down to that.

But it is very worrying if whoever installed it had not properly tightened things up!
 
Sometimes a bad connection can cause a surge as it reconnects on to a load which might just trip things. But hopefully you have checked ALL of the terminals for tightness now and it might be down to that.

But it is very worrying if whoever installed it had not properly tightened things up!
Only thing is the poor connections were on other circuits, so i wasn't sure how they could affect the sockets. But you're right, very worryihg. I'm in a rental property so i wouldnt be surprised if any EICRs were of the drive-by variety
 

Reply to Mystery tripping during the night in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hey all, I'm looking for some advice to help me troubleshoot my strange issue with my consumer unit/fuse board on which my RCD keeps tripping...
Replies
25
Views
2K
Hi Guys, I'm having trouble diagnosing a fault on a customers downstairs socket ring, which only ever trips when the washing machine is used. The...
Replies
22
Views
3K
I'm writing this mainly hoping something occurs to me while writing it! I got called to an occasionally tripping RCD. It's a Hager double height...
Replies
19
Views
2K
Woke up this morning and tried to turn on the computer (work from home) wouldn't power on, checked lights they worked fine. Went downstairs to...
Replies
21
Views
3K
Called out to fault on RCD tripping maybe twice in a month for sometime. Did all the tests & found RCD was faulty, Refitted a new Rcd Type A which...
Replies
2
Views
882

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock