Called out to fault on RCD tripping maybe twice in a month for sometime.
Did all the tests & found RCD was faulty, Refitted a new Rcd Type A which made matters worst.
So refitted original RCD Type AC for the time being.
Insulation Resistance measurements were 20 M ohms.
Ring continuity fine too.
Testing proved difficult because of RCD tripping even with my Socket Tester, then everything went back to normal, power back on & days later still on.
Obviously Client not happy & believe’s ive done something.
The DB is a Stack DB,Crabtree Starbreaker all cabling brand new.
Its Split between Top & Bottom Main Switch mcb’s
Bottom RCD 30ma 80amp supplying 5 Ring Mains & 3 other Radial circuits MCB’s
i think I narrowered it down to-the kitchen/dining RM & UNPLUGGED all equipment but doing this the RCD still tripped.
Fingers crossed no call outs over Xmas… returning after hols … Any ideas fellow Sparkies😎
 
How did you ascertain that the original rcd was faulty? Did you test the original rcd with outgoing circuits disconnected? If you havnt got an earth leakage clamp meter you can connect one circuit back at a time and use ramp test on your mft with no circuits connected, note the ma, then add back one at a time to see when its requiring less ma to trip, could point you in the right direction
 

Reply to RCD Tripping intermittently in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I'm writing this mainly hoping something occurs to me while writing it! I got called to an occasionally tripping RCD. It's a Hager double height...
Replies
19
Views
2K
I just finished a garden room supply. The customer already had a CPN garage consumer unit that the last sparks left there, brand new in box, and...
Replies
2
Views
877
Hi Guys, I'm having trouble diagnosing a fault on a customers downstairs socket ring, which only ever trips when the washing machine is used. The...
Replies
22
Views
3K
Hey all, I'm looking for some advice to help me troubleshoot my strange issue with my consumer unit/fuse board on which my RCD keeps tripping...
Replies
25
Views
2K
Hi all, Grateful for your expertise regarding my confusion on the below. Context: French rural domestic property Single phase supply, TT...
Replies
12
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock