Search the forum,

Discuss Need help about Surge Protective Device in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
0
Recently I have installed Type 2 Surge Protective Device SPD 20 to 40kA, Type1+2, Phase + Neutral + Earth (2 Pole 275 Volt AC) (Uc-275VAC, In-20KA, Imax-40KA, Up ≤ 1.5 KV) after 64A DP MCB at home MDB. The home lode is around 1.75KW. We have 220 VAC main line here.

At the evening of 3rd day after installation, the SPD was exploded. I find that the cartridge of Phase side was damaged and it was totally short with earthing terminal. But cartridge of neutral side was in good condition. There was no sign of lightning nearby. No neighbour was affected with Spikes and surges at that time. I am confused about the reason how the SPD got damaged!

Now I am going to replace the SPD with “Type 2 Surge Protective Device SPD (Phase side: Uc-320VAC, In-20KA, Imax-40KA, Up ≤ 1.5 KV Neutral Side: Uc-255VAC, In-20KA, Imax-40KA, Up ≤ 1.5 KV). Will it be good?

Thanks.
 
A starting point is what make/model of SPD did you fit? A photo might help here.

Normally SPD have internal thermal fuses to deal with overheating, and for worst-case protection they depend on either the incoming supply's over-current protection, or for smaller SPD they depend on a MCB just for the SPD.

SPD are designed to deal with very short-term surges, so tens of microseconds from induced lightning current or the switching of large motors, etc. Where they are at serious risk of overheating is when you have a long-duration over-voltage situation, for example, a power cross situation (when a HV cable falls and strikes a LV cable) or an open neutral in an unbalanced 3-phase system, etc.

However, any reputable SPD should fail safe in such conditions with the internal thermal fuse (basically solder joint) opening to disconnect before it reaches a dangerous temperature.

What will case even a good SPD to fail catastrophically is a short surge beyond its energy handling limits, but that is unusual outside of a direct lightning strike the the building, or to a strike to an overhead power line within a km or so of the SPD. You are down as from India, that has more thunderstorm days than the UK where I am by an order of magnitude but I guess it varies dramatically over your country.
 
Last edited:
A starting point is what make/model of SPD did you fit? A photo might help here.

Normally SPD have internal thermal fuses to deal with overheating, and for worst-case protection they depend on either the incoming supply's over-current protection, or for smaller SPD they depend on a MCB just for the SPD.

SPD are designed to deal with very short-term surges, so tens of microseconds from induced lightning current or the switching of large motors, etc. Where they are at serious risk of overheating is when you have a long-duration over-voltage situation, for example, a power cross situation (when a HV cable falls and strikes a LV cable) or an open neutral in an unbalanced 3-phase system, etc.

However, any reputable SPD should fail safe in such conditions with the internal thermal fuse (basically solder joint) opening to disconnect before it reaches a dangerous temperature.

What will case even a good SPD to fail catastrophically is a short surge beyond its energy handling limits, but that is unusual outside of a direct lightning strike the the building, or to a strike to an overhead power line within a km or so of the SPD. You are down as from India, that has more thunderstorm days than the UK where I am by an order of magnitude but I guess it varies dramatically over your country.
 

Attachments

  • Euro.jpg
    49 KB · Views: 11
This might also be worth considering:
What is your opinion about this
 
What is your opinion about this
It is not a brand that I know, but on the appearance it would look like a good enough choice for most situations where you do not expect a direct strike.

Type 2 SPD are for induced surges, i.e. nearby strike, whereas Type 1 or Type 1+2 are able to cope with higher energy surges from a hit to the building's lightning protection system, or to an overhead cable some distance away.
 

Reply to Need help about Surge Protective Device in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, Grateful for your expertise regarding my confusion on the below. Context: French rural domestic property Single phase supply, TT...
Replies
12
Views
2K
Is there a reason why these surge protective devices come with 2 neutral links?
Replies
10
Views
2K
BACKGROUND I live in a small town where it is difficult to find ceritified electricians. In fact, electrician certification is not common for...
Replies
1
Views
1K
Hello, I have a Clipsal consumer unit with two "ways" unused and blanked off and potentially a third available as the Proteus Geyer B16 MCB is...
Replies
16
Views
4K
  • Article
Electrical2Go - Electric Car Charging at Home - Comprehensive Guide As EV ownership and the transition towards electric cars rise, having a home...
Replies
0
Views
243

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock