Neutral-Earth voltage

Discuss Neutral-Earth voltage in the UK Electrical Forum area at ElectriciansForums.net

leep82

-
Arms
Reaction score
131
Called to a property yesterday after the customer had been advised to call an electrician by an engineer who had done some work on there cooker. I arrived and was directed towards a socket in the kitchen. The lady couldnt really explain what the engineer had told her.

I plugged my multifunction tester in and immmediately realised there was a problem. The display wasnt showing a voltage between live and earth but was showing voltage between live-neutral and neutral-earth. I removed the socket front and saw that the live and neutral conductors had been connected into the wrong terminals. Once i had sorted this out i plugged my tester in again to try and do a Zs test, but i was unable to as there was still voltage showing between neutral and earth. I tried another socket in the kitchen on the same circuit and was able to perform the test, getting a reading of 500ohms. The system is a TT although a quick look at the mains suggests there might be PME available.

I went around various sockets on the circuit and was left a little bit baffled as some would let me perform a Zs test and others wouldnt as it was indicating a voltage between neutral and earth. When i initially removed the socket with reversed polarity i used my tester across neutral and earth and was getting a voltage of around 30v. I have advised the customer to have a EICR, which she is going ahead with. I wasnt able to spend any great deal of time there last night so sorry for any lack of other information. As already said i will be returning to carry out an EICR so will hopefully get to the bottom of the issue then, but in the meantime any suggestions, advice greatly welcomed.
 
Did they build the stairs around the DB?
That is a tight space and with that stupid shaped shelf that doesn't help changing the board will be as much work if not more!
Question 2 Is the husband still around or has she buried him?
 
Did they build the stairs around the DB?
That is a tight space and with that stupid shaped shelf that doesn't help changing the board will be as much work if not more!
Question 2 Is the husband still around or has she buried him?
Yeah he's still around, he was giving it the " i dont know why she wants this work done its been fine for years " line, when i was there. Thinking of moving the DB directly under that shelf if possible. I certainly wouldnt want to keep it in there
 
The customer is aware that if they require a satisfactory report then they are going to have to spend more money to have the remedial work done. Once i have copied the report from draft form i am going to have a sit down with them to discuss there options

I think I'd get my bill in before talking though any of it with them to be honest
 

Reply to Neutral-Earth voltage in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock