New circuits wired into a plastic consumer unit

Discuss New circuits wired into a plastic consumer unit in the UK Electrical Forum area at ElectriciansForums.net

TJC1

-
Reaction score
6
Had to install a ring main & cooker circuit for a new kitchen we have been doing.

The consumer unit is hager split load but is plastic. There is no room in the cupboard to add another board and the customers dont want to pay for a board change.

I guess i could just note on the form saying customers did not want to change to metal?
 
Which form are you implying?
That plastic board does not comply with the current regs.i hope you have advised them.
I wouldn't do that job unless if they agree to the change of the board.
Are you signing off any certs taking full responsibility just in case something happens?
You have installed 2 circuits a rfc and cooker radial.
You need EIC and everything has to comply with the current regs.
You cannot sign of the EIC with a plastic CU.
What a load of rubbish that statement is.
You are responsible for your work carried out only.
A simple note on the eic commenting on the CU is all that is needed.
You are advised to check the connections and condition of the CU and if it’s fit for continued service then it’s acceptable to leave it.
To tell people they must have it renewed or work can’t be carried out is just plain unethical and deceiving in my opinion.
You will find a section in the on site guide explaining this very topic of installing new circuits from an existing plastic CU
 
Last edited:
Which form are you implying?
That plastic board does not comply with the current regs.i hope you have advised them.
I wouldn't do that job unless if they agree to the change of the board.
Are you signing off any certs taking full responsibility just in case something happens?
You have installed 2 circuits a rfc and cooker radial.
You need EIC and everything has to comply with the current regs.
You cannot sign of the EIC with a plastic CU.

Do you always tell customers they need a metal consumer unit fitting if you are doing electrical work in their properties?
 
I advise them and point out the safety issue strongly.
Most of them don't know the regulations and have no clue about the updates.
Most of them listen and book me in to change their CUs.
It is all very well pointing out how the Regs have changed but if you're putting this across in such a way they are opting for a consumer unit change then you need to consider your ethics.
 
What a load of rubbish that statement is.
You are responsible for your work carried out only.
A simple note on the eic commenting on the CU is all that is needed.
You are advised to check the connections and condition of the CU and if it’s fit for continued service then it’s acceptable to leave it.
To tell people they must have it renewed or work can’t be carried out is just plain unethical and deceiving in my opinion.
You will find a section in the on site guide explaining this very topic of installing new circuits from an existing plastic CU
Excuse me i don't say "MUST".
I say to them it needs to be changed to comply to the current regs.
Most of them take my word.
You can be mad at my way of working but that is me very keen at safety so i do it ~100%.
Uou can sceream as much as you want but that is how i have been trained to carry out my work.
I don't carry out sub standard work.
I rather not do it than loose my credibility.
 
No one is doubting your standards of workmanship but as dpg states where do you stop? Are you now fitting rcd/rcbos to every lighting circuit even if not adding or altering?
 
Excuse me i don't say "MUST".
I say to them it needs to be changed to comply to the current regs.
Most of them take my word.
You can be mad at my way of working but that is me very keen at safety so i do it ~100%.
Uou can sceream as much as you want but that is how i have been trained to carry out my work.
I don't carry out sub standard work.
I rather not do it than loose my credibility.
It’s very admirable that you install to a high Standard however the fact is it doesn’t need to be changed if fit for purpose.
There is no law requiring that an electrical installation requires upgrading to the latest standard.
It’s like saying that if you see red and black coloured wiring, then you refuse to do any alterations unless it’s all ripped out and rewired.
 
It’s very admirable that you install to a high Standard however the fact is it doesn’t need to be changed if fit for purpose.
There is no law requiring that an electrical installation requires upgrading to the latest standard.
It’s like saying that if you see red and black coloured wiring, then you refuse to do any alterations unless it’s all ripped out and rewired.
Don't get me wrong i have changed CUs with old colour codes after taking all tests to confirm the wiring is safe ie continuity and IR.So after those test i can carry on and change the CU to the required standard.Sometimes the tails are not the required size.
If i do tests on the installation and find that it is not up to scrach i will advise accordingly i e to rewire depending on the nature of the install.
Luckly my clients get it most of the time.
 
That’s the book not a reg no?
Reg no will be quoted when i am in court.
What are you getting taken to court for ?
Obtaining monies by deception ? ;):D
You wanted the reg no. and i am saying i will not telling you the reg no since you are a qualified Electrician who should know better.
I will quote it in court to those who have no clue abt it if they happen to ask.
 
Don't get me wrong i have changed CUs with old colour codes after taking all tests to confirm the wiring is safe ie continuity and IR.So after those test i can carry on and change the CU to the required standard.Sometimes the tails are not the required size.
If i do tests on the installation and find that it is not up to scrach i will advise accordingly i e to rewire depending on the nature of the install.
Luckly my clients get it most of the time.
I think your clients are definitely getting it.
 
1983F593-C0EF-4406-ACC3-B1F2608BBA19.jpeg
They amended it and what was not ammended was just carried over.
I can understand what your problem is but i know exactly what i am doing/talking about.
I am 18th edition trained as well.
 

Reply to New circuits wired into a plastic consumer unit in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock