Richard Knight
Hello,
We purchased a plot of land a while ago and we are trying to establish how we can actually connect into the mains transformer mast which is available on site.
Originally we had 3 options. There was a Scottish power owned cable that we could tap into this would cost £4500.00 to link to just our plot as it would be over 150m distance. Or each plot owner could take their own supply from the mast and have a single 100amp connection which would be metered and then extended using the private cable laid which links it to our plot £1200.00.
Or all the plot owners could chip in together on a communal solution - distribution fuse board?
Scottish power have said that if everyone does one of the first two options then there wouldn't be enough capacity on the transformer mast to supply everyone... So we have asked them to price for the distribution fuse board.
This is what they are pricing for:
We shall install and connect a 400v low voltage three phase cable from the LV pole, install a 9 way DFB, install 9 x 2m x 25mm LSOH cables from DFB to new cut outs, reconnect and energise the existing meter to one of the new cutouts. Our works will include 22m of service cable. All excavation, backfill and reinstatement will be carried out by the customer.
When I spoke to them on the phone they told be that this will give 9 x 60 amp connections (all separately metered) 100 amp cable head into the DFB, the DFB is protected by an 80 amp fuse and then each cutout of the DFB is protected by a 60 amp fuse...
I want to check that that means that all 9 properties can draw of 60 amps at the same time?
They have priced £4500.00 inc VAT for the works, seems quite a lot but I guess these things do cost allot! £458.00 of work is non contestable but the rest could be done by an approved company of a list they gave us... Do people think it's a fair price or should I try and get some further quotes?
Any advice is greatly appreciated!
We purchased a plot of land a while ago and we are trying to establish how we can actually connect into the mains transformer mast which is available on site.
Originally we had 3 options. There was a Scottish power owned cable that we could tap into this would cost £4500.00 to link to just our plot as it would be over 150m distance. Or each plot owner could take their own supply from the mast and have a single 100amp connection which would be metered and then extended using the private cable laid which links it to our plot £1200.00.
Or all the plot owners could chip in together on a communal solution - distribution fuse board?
Scottish power have said that if everyone does one of the first two options then there wouldn't be enough capacity on the transformer mast to supply everyone... So we have asked them to price for the distribution fuse board.
This is what they are pricing for:
We shall install and connect a 400v low voltage three phase cable from the LV pole, install a 9 way DFB, install 9 x 2m x 25mm LSOH cables from DFB to new cut outs, reconnect and energise the existing meter to one of the new cutouts. Our works will include 22m of service cable. All excavation, backfill and reinstatement will be carried out by the customer.
When I spoke to them on the phone they told be that this will give 9 x 60 amp connections (all separately metered) 100 amp cable head into the DFB, the DFB is protected by an 80 amp fuse and then each cutout of the DFB is protected by a 60 amp fuse...
I want to check that that means that all 9 properties can draw of 60 amps at the same time?
They have priced £4500.00 inc VAT for the works, seems quite a lot but I guess these things do cost allot! £458.00 of work is non contestable but the rest could be done by an approved company of a list they gave us... Do people think it's a fair price or should I try and get some further quotes?
Any advice is greatly appreciated!