Good evening

following a visual inspection in a property that had an electrical fire in the fuse board area
obviously i could not actually test anything, but visually identified that the lighting circuits had no earth (not even cut back)
now the insurance company ideally want a new distribution board and all the circuits being cut back to where they are not damaged then extended back and re-connected

so my question is:
all the pendents and switches are plastic, but really don't think i can join on to and extend the old cable that contains no cpc

or am i wrong?

am i right in thinking they have no choice but to get the lighting re-wired

thanks guys
 
rewire the lights. you can't reconnect/joint to cables that don't comply with current regs. are the insurers penny pinching?
 
so what do you do if your on a consumer unit change and lighting circuits dont have cpc?? If there are no metal accessories or metal back boxes i dont see the problem reconecting.
I seem to recall reading in the Regs that all point must have a cpc present, or words to that effect!!
 
can you get me the reg number on that? Were not talking about installing without cpc,reconnection of existing circuits is in question..
Not got my regs with me, but common sense will, or should tell you that, part of the testing regime is to prove the cpc continuity on to on top of that how are you going to test Zs at lighting points with nil cpc that's why it shouldn't be reconnected, your name will be on the cert wont ? you will be the last person working on the installation, your responsibility, hate to be in your shoes when you are in front of his Honour if some poor person gets a belt from an unearthed lighting circuit.
 
so what do you do if your on a consumer unit change and lighting circuits dont have cpc?? If there are no metal accessories or metal back boxes i dont see the problem reconecting.

Discuss it with the customer and if they decline to have the installation brought up to a safe standard then decline the work.

In exceptional circumstances I might consider the ESC's suggestion for what to do in exceptional circumstances, but in normal circumstances no.

The problem is quite simply that it does not comply with the current wiring regulations, nor does it comply with a fair minimum standard based on the wiring regulations. The installation of a cpc to every point of connection is a basic requirement for safety and has been for a long time.
[automerge]1579210458[/automerge]
Good evening

following a visual inspection in a property that had an electrical fire in the fuse board area
obviously i could not actually test anything, but visually identified that the lighting circuits had no earth (not even cut back)
now the insurance company ideally want a new distribution board and all the circuits being cut back to where they are not damaged then extended back and re-connected

so my question is:
all the pendents and switches are plastic, but really don't think i can join on to and extend the old cable that contains no cpc

or am i wrong?

am i right in thinking they have no choice but to get the lighting re-wired

thanks guys

Write a letter explaining the situation and why further work is required for the installation to comply with current regulations
 
Not got my regs with me, but common sense will, or should tell you that, part of the testing regime is to prove the cpc continuity on to on top of that how are you going to test Zs at lighting points with nil cpc that's why it shouldn't be reconnected, your name will be on the cert wont ? you will be the last person working on the installation, your responsibility, hate to be in your shoes when you are in front of his Honour if some poor person gets a belt from an unearthed lighting circuit.
Discuss it with the customer and if they decline to have the installation brought up to a safe standard then decline the work.

In exceptional circumstances I might consider the ESC's suggestion for what to do in exceptional circumstances, but in normal circumstances no.

The problem is quite simply that it does not comply with the current wiring regulations, nor does it comply with a fair minimum standard based on the wiring regulations. The installation of a cpc to every point of connection is a basic requirement for safety and has been for a long time.
[automerge]1579210458[/automerge]


Write a letter explaining the situation and why further work is required for the installation to comply with current regulations


Lighting circuits installed before 1966 did not require a circuit protective conductor (cpc) to be run to and terminated at every point and accessory of a lighting circuit, as is currently required by Regulation 411.3.1.1 of BS 7671.

It should be remembered that the Wiring Regulations are not retrospective, as is clearly mentioned in a note in the introduction to BS 7671 which states: Existing installations that have been installed in accordance with earlier editions of the Regulations may not comply with this edition in every respect. This does not necessarily mean they are unsafe for continued use or require upgrading.


Therefore, there is no legal requirement, and no regulation in BS 7671, requiring an existing lighting circuit to be rewired or upgraded to current standards. However, it is essential that the safety of the installation is not compromised when any alteration and/or addition is carried out.

taken from elecsa.
 
As far as I was aware, if you are modifying a circuit then you just make sure it now complies?

Would the same principal apply if say you were adding a spur socket onto a RFC that has no RCD protection? Would you need to protect the circuit with an RCD or just protect that outlet with an RCD?
 
In my opinion if I were in your shoes I would tell the insurance company that the lighting circuit/s need to be rewired why delay the inevitable they are going to have to be rewired in the coming years and now would be the ideal time it annoys me when people try looking for ways out of doing the sensible and right thing tell them that you are going to be the one to certify the work and don’t want any repercussions after you’ve left the job. They’ll be quick enough to point the finger at you if anyone had a belt after you’ve left.
 
It should be remembered that the Wiring Regulations are not retrospective, as is clearly mentioned in a note in the introduction to BS 7671 which states: Existing installations that have been installed in accordance with earlier editions of the Regulations may not comply with this edition in every respect. This does not necessarily mean they are unsafe for continued use or require upgrading.

This is a commonly misunderstood extract from BS7671, a lot of people don't seem to understand clear written English and much prefer to see what they think is written there.
Forget your preconceived idea of what 8s written there and re-read it. Take the time to understand exactly what is written.


"This does not necessarily mean they are unsafe for continued use or require upgrading"
This does not say that all work carries out to previous editions of the regulations is safe for continued use, nor does it say that it is exempt from any requirement to upgrade.
What it says is that complying with a previous edition does not necessarily make it unsafe, that means that compliance with a previous edition alone does not make something unsafe. It means that compliance with a previous edition could be safe or unsafe, it could be safe if the changes to the regulations do not reflect a safety improvement (such as changing from red/black to brown/blue) or it could be unsafe if the changes to the regulations reflect a previous method having been found to be dangerous (such as putting fuses in the neutral). Alternatively it could be that the changes in the regulations reflect an improvent in the safety of the installation, such as the case of old lighting circuits not being earthed.

Acgording to BS7671 any work carried out to an existing installation must only be carried out after confirming that the existing installation is in a safe condition, including earthing and bonding being correct, and bringing it up to current standards if necessary.
 
@davesparks so on this principle you would not give a satisfactory report if cables buried within walls are not on 30mA rcd? If upgrading a consumer unit and the lighting circuit has no earth and has no metal switchgear ect then this is perfectly acceptable with a sticker on the cu stating this. I agree the better option always would be to rewire the circuit but i dont belive you saying it has to be rewired i think you could be seen as trying to generate work.

As far as I was aware, if you are modifying a circuit then you just make sure it now complies?

Would the same principal apply if say you were adding a spur socket onto a RFC that has no RCD protection? Would you need to protect the circuit with an RCD or just protect that outlet with an RCD?

if you wanted to add a socket outlet to a rfc that no had rcd protection would you rewire it? Change the cu or add some surface wiring to an rcd socket outlet? I would say the final decision is the customers.
 
As far as I was aware, if you are modifying a circuit then you just make sure it now complies?

Would the same principal apply if say you were adding a spur socket onto a RFC that has no RCD protection? Would you need to protect the circuit with an RCD or just protect that outlet with an RCD?
Discuss it with the customer and if they decline to have the installation brought up to a safe standard then decline the work.

In exceptional circumstances I might consider the ESC's suggestion for what to do in exceptional circumstances, but in normal circumstances no.

The problem is quite simply that it does not comply with the current wiring regulations, nor does it comply with a fair minimum standard based on the wiring regulations. The installation of a cpc to every point of connection is a basic requirement for safety and has been for a long time.
[automerge]1579210458[/automerge]


Write a letter explaining the situation and why further work is required for the installation to comply with current regulations
Agree with Davesparks
[automerge]1579248135[/automerge]
Lighting circuits installed before 1966 did not require a circuit protective conductor (cpc) to be run to and terminated at every point and accessory of a lighting circuit, as is currently required by Regulation 411.3.1.1 of BS 7671.

It should be remembered that the Wiring Regulations are not retrospective, as is clearly mentioned in a note in the introduction to BS 7671 which states: Existing installations that have been installed in accordance with earlier editions of the Regulations may not comply with this edition in every respect. This does not necessarily mean they are unsafe for continued use or require upgrading.


Therefore, there is no legal requirement, and no regulation in BS 7671, requiring an existing lighting circuit to be rewired or upgraded to current standards. However, it is essential that the safety of the installation is not compromised when any alteration and/or addition is carried out.

taken from elecsa.
Think you have to understand which may conflict with your post, CU change requires an EIC can't see how you could honestly issue an EIC with a satisfactory conclusion when connecting an un earthed lighting circuit to the new CU, what are your thoughts on that???
 
Last edited:
Lighting circuits installed before 1966 did not require a circuit protective conductor (cpc) to be run to and terminated at every point and accessory of a lighting circuit, as is currently required by Regulation 411.3.1.1 of BS 7671.

It should be remembered that the Wiring Regulations are not retrospective, as is clearly mentioned in a note in the introduction to BS 7671 which states: Existing installations that have been installed in accordance with earlier editions of the Regulations may not comply with this edition in every respect. This does not necessarily mean they are unsafe for continued use or require upgrading.


Therefore, there is no legal requirement, and no regulation in BS 7671, requiring an existing lighting circuit to be rewired or upgraded to current standards. However, it is essential that the safety of the installation is not compromised when any alteration and/or addition is carried out.

taken from elecsa.

I also sort guidance when trying to understand the writings of BS7671.

Electrical Safety First Best Practice Guide 1, also gives some guidance; https://www.electricalsafetyfirst.org.uk/media/1203/best-practice-guide-1-issue-3.pdf

Indent 10.7, if this is in a domestic property.
 
The best practice guide is clear. When changing a consumer unit and lighting circuits with no cpc exist, they should only be reconnected when all other remedial actions are refused.
Are the insurers going to refuse rewiring from a liability point of view when the electrician says this is the best and safest method, and to not do so would not be fully compliant with the wiring regulations but would just about be safe if no-one changes any accessories ?
 
The best practice guide is clear. When changing a consumer unit and lighting circuits with no cpc exist, they should only be reconnected when all other remedial actions are refused.
Are the insurers going to refuse rewiring from a liability point of view when the electrician says this is the best and safest method, and to not do so would not be fully compliant with the wiring regulations but would just about be safe if no-one changes any accessories ?
Personally I think the rulings need updating: You are changing a CU in Mrs Ordinaries' House after a house fire. oh dear no cps in the lighting wiring, after explaining that some remedial wiring need doing ergo rewiring the lights before I can reconnect.
How long is it going to take the Insures to agree to that? weeks, maybe in the meantime the Home owners are without any lights The BP Guide is right in some respects, but there needs to be better guidelines in my opinion for what it's worth. on how to proceed, all very well telling Mrs Ordinary not to use any metal or conductive accessories, but you know what most homeowners are like, oh that's a nice light fitting won't that look nice in our lounge ???
 
Personally I think the rulings need updating: You are changing a CU in Mrs Ordinaries' House after a house fire. oh dear no cps in the lighting wiring, after explaining that some remedial wiring need doing ergo rewiring the lights before I can reconnect.
How long is it going to take the Insures to agree to that? weeks, maybe in the meantime the Home owners are without any lights The BP Guide is right in some respects, but there needs to be better guidelines in my opinion for what it's worth. on how to proceed, all very well telling Mrs Ordinary not to use any metal or conductive accessories, but you know what most homeowners are like, oh that's a nice light fitting won't that look nice in our lounge ???
I agree that in these emergency circumstances after a fire, getting the power back on is the priority.

I don't agree with the best practice guide though that a cpc free circuit should be reconnected on a planned consumer unit change, even if the customer is fully briefed as to the safety implications.

I'd be laying it on thick to the insurance if it were me pushing for rewiring.
 
So looking at indent 10.7, it seems it is not permitted to reconnect a cpc free circuit when changing a CU as there is no supervision to ensure that nobody swaps accessories for conductive ones!!
 
The ESF Best Practice Guide 1, actually states the opposite for a domestic dwelling, indent 10.7.
It very much does.

This info seems to be at odds with flow chart A2 which states that in a planned CU change situation the affixing of a label to the CU telling users not to change accessories is enough to give the CU change the go ahead.
This chart appears to be for use in dwellings, as mentioned in indent 10.7, as the last step is to notify the work. This step would not be applicable to other installations apart from dwellings.
 
So looking at indent 10.7, it seems it is not permitted to reconnect a cpc free circuit when changing a CU as there is no supervision to ensure that nobody swaps accessories for conductive ones!!
That’s why it’s important to attach a warning label at the CU stating that no class 1 accessories are to be fitted to the lighting circuit with no cpc.
Don’t know who came up with such a label tho as it’s not in bs7671?
 
That’s why it’s important to attach a warning label at the CU stating that no class 1 accessories are to be fitted to the lighting circuit with no cpc.
Don’t know who came up with such a label tho as it’s not in bs7671?

Does a label class as effective supervision though ?

If the end user cannot be trusted to heed information imparted verbally and written on a certificate, what magic exists in the label to change things ?
 
So looking at indent 10.7, it seems it is not permitted to reconnect a cpc free circuit when changing a CU as there is no supervision to ensure that nobody swaps accessories for conductive ones!!

Your never going to stop diy taking place, even if there is a cpc there they may not connect it, you cant stop everything, we dont put sockets in bathroom but that doesn't stop someone putting an extension lead in the bath!!?
 
Does a label class as effective supervision though ?

If the end user cannot be trusted to heed information imparted verbally and written on a certificate, what magic exists in the label to change things ?
Because the regulations assume electrical work to be carried out by competent persons electrically skilled.
a warning label clearly on view at the CU should not be missed by anyone skilled carrying out electrical work as the lighting would be isolated at the CU. However we don’t live in the fairytale that bs7671 wants us all to live in and the inevitable DIY jobs will ignore the warnings.
Like I said tho I’m not sure where this requirement for the label has gone from?
I’m assuming the ESC / best practice guide to which the likes of Napit and the Niceic seem to endorse this warning label method as a last resort.
No I don’t think a warning label will be classed as suitable supervision as it’s not under the control of skilled or instructed persons
 
Because the regulations assume electrical work to be carried out by competent persons electrically skilled.
a warning label clearly on view at the CU should not be missed by anyone skilled carrying out electrical work as the lighting would be isolated at the CU. However we don’t live in the fairytale that bs7671 wants us all to live in and the inevitable DIY jobs will ignore the warnings.
Like I said tho I’m not sure where this requirement for the label has gone from?
I’m assuming the ESC / best practice guide to which the likes of Napit and the Niceic seem to endorse this warning label method as a last resort.
ELECTRIC MAGIC!!!! !!!!
 

Reply to No CPC in lighting circuits / Fire damage in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock