Currently reading:
Only 2 brands for domestic type A rcd/rcbo + type 2 spd in board??

Discuss Only 2 brands for domestic type A rcd/rcbo + type 2 spd in board?? in the Electrical Tools and Products area at ElectriciansForums.net

Mattja

-
Reaction score
10
Looking around I'm wondering if I'm going mad. Would have thought type 2 spd next to main switch and type A (not type AC) rcd/rcbos would be the standard everyone should be looking for now (even if it's just recommended and not strictly required in domestics). But only Wylex and Schneider seem to supply the parts?

Anyone else found a supplier for both these features from any other brands or is this it?
 
Hager do it.

In fact they have made Type A RCCBs and RCBOs for very many years indeed. However these were not common in the UK in the past. The UK is years behind much of the world in this regard.
 
Cheers, a shame that it's Hager. I refuse to buy a Hager board until they stop mucking about with those stupid rectangular knockouts. Every other brand I've used has standard sizes of circular knockouts that grommets and glands can fit into, just Hager that insists I waste time and materials terminating SWA in a separate enclosure and worry about having enough cables through each side/top/bottom knockout to fill the hole enough for IP rating and then mess around with intumescent sealant when I should just be able to put an intumescent grommet/gland in there and be done with it quick and neat!

And yes it's bizarre isn't it? They do these parts for many other countries, surely it can't be that hard for manufacturers to put existing components into a form that fits UK boards.
 
Cheers, a shame that it's Hager. I refuse to buy a Hager board until they stop mucking about with those stupid rectangular knockouts. Every other brand I've used has standard sizes of circular knockouts that grommets and glands can fit into, just Hager that insists I waste time and materials terminating SWA in a separate enclosure and worry about having enough cables through each side/top/bottom knockout to fill the hole enough for IP rating and then mess around with intumescent sealant when I should just be able to put an intumescent grommet/gland in there and be done with it quick and neat!

And yes it's bizarre isn't it? They do these parts for many other countries, surely it can't be that hard for manufacturers to put existing components into a form that fits UK boards.

You can get Hager boards with circular knockouts and without any knockouts.
 
just Hager that insists I waste time and materials terminating SWA in a separate enclosure and worry about having enough cables through each side/top/bottom knockout to fill the hole enough for IP rating and then mess around with intumescent sealant when I should just be able to put an intumescent grommet/gland in there and be done with it quick and neat!

Hager don't insist that you waste time or materials, they supply boards with rectangular or circular knockouts or with plain sides. If you order boards with rectangular knockouts it's hardly their fault.

As for intumescent sealants, why would you need them?
 
I've only found them with rectangular knockouts going into wholesalers and looking at pictures on webpages. If they're not displayed or advertised with circular knockouts it's their fault that I'm assuming they're all with rectangular knockouts. Good to know they can be found somewhere, cheers, but hardly an unfair assumption on my part.

As for sealants, if I'm putting up a metal board that's meant to contain a fire then surely it's good practise not to leave holes in it, and if I'm going down that route, best go intumescent so I'm not wasting time. I'm not having a go if you're not sealing it up, your choice, but I think it's better to do so (and for round knockouts it's as quick and easy as pushing a grommet in).
 
I've only found them with rectangular knockouts going into wholesalers and looking at pictures on webpages. If they're not displayed or advertised with circular knockouts it's their fault that I'm assuming they're all with rectangular knockouts. Good to know they can be found somewhere, cheers, but hardly an unfair assumption on my part.

As for sealants, if I'm putting up a metal board that's meant to contain a fire then surely it's good practise not to leave holes in it, and if I'm going down that route, best go intumescent so I'm not wasting time. I'm not having a go if you're not sealing it up, your choice, but I think it's better to do so (and for round knockouts it's as quick and easy as pushing a grommet in).

Its not their fault that you haven't properly researched an dspecified the equipment you will be installing, if you are designing the installation then you are responsible.

Why is it meant to contain a fire? Metal CUs don't have any fire rating or type testing for containment of fire.
 
ESR also do a type A RCD and at a reasonable price. I think Chint do a type A also, although i would not buy Chint as I believe they fail more often than most RCD's.
 
Hi MCG offer a type 2 & 3 combined SPD for a good price (£48 inc vat) single module you can get from CEF,
I have found these to be very good value.
 
Looking around I'm wondering if I'm going mad. Would have thought type 2 spd next to main switch and type A (not type AC) rcd/rcbos would be the standard everyone should be looking for now (even if it's just recommended and not strictly required in domestics). But only Wylex and Schneider seem to supply the parts?

Anyone else found a supplier for both these features from any other brands or is this it?
Hi,
Looks like this thread is a few months old but ,
I use a the “Fusebox” boards( consumer units ) now for all my installs , THey have type A rcbo s and a type 2 SPD built in next to the main switch , solid board and only £12 per rcbo

£120 all in for 8 way rcbo and SPD .
?
 
Hi,
Looks like this thread is a few months old but ,
I use a the “Fusebox” boards( consumer units ) now for all my installs , THey have type A rcbo s and a type 2 SPD built in next to the main switch , solid board and only £12 per rcbo

£120 all in for 8 way rcbo and SPD .
?
I’ve heard ( happy to be corrected) that fuse box have no ocpd for their SPD over than using the DNO fuse ( no internal ocpd on the SPD either) , for this reason I wouldn’t use them if wanting an SPD in the board.
 
Last edited:
I’ve heard ( happy to be corrected) that fuse box have no ocpd for their SPD over than using the DNO fuse ( no internal ocpd on the SPD either) , for this reason I wouldn’t use them if wanting an SPD in the board.
I’ve heard ( happy to be corrected) that fuse box have no ocpd for their SPD over than using the DNO fuse ( no internal ocpd on the SPD either) , for this reason I wouldn’t use them if wanting an SPD in the board.

Hi Ian,
Yes you are correct in saying their is no internal ocpd but they are rated at 125a which for most domestic installs with 60 and 80amp cutouts, the DNO fuse is acceptable for last resort OCPD with less than 250mm 6mm cable in total on the internal LNE SPD cables. For an extra £3 a 32amp mcb can be added to supply the SPD to give protection aswell ?
 
Hi Ian,
Yes you are correct in saying their is no internal ocpd but they are rated at 125a which for most domestic installs with 60 and 80amp cutouts, the DNO fuse is acceptable for last resort OCPD with less than 250mm 6mm cable in total on the internal LNE SPD cables. For an extra £3 a 32amp mcb can be added to supply the SPD to give protection aswell ?
My issue is continuity of service, if an SPD relies upon the dno fuse and for whatever reason it shorts out then you will loose the total supply and will be non compliant.
The extra £3 for mcb sounds okay tho.
 
My issue is continuity of service, if an SPD relies upon the dno fuse and for whatever reason it shorts out then you will loose the total supply and will be non compliant.
The extra £3 for mcb sounds okay tho.
TBF, that’s a good point and totally agree Ian, Fitted one earlier this week with SPD and personally did opt for the 32a mcb as was a 100A supply fuse , may consider this for 60-80a aswell. Also fitted an AXIOM earlier this week with SPD and manufactures instructions required ocpd via mcb, maybe fusebox will require this soon aswell.
but to answer the ops question , the brand is an option with type A rcbo s and type 2 SPD , ( with optional mcb ocpd ) and is a good build quality at a reasonable cost . ??
 
It really depends on the SPD whether it needs an OCPD.
Its my understanding that SPDs are designed to fail open circuit. Pretty sure they are manufactured with a small soldered joint which is spring loaded, this is designed to melt under high fault currents and break the contact.
 
I was going to look inside one, to see exactly what is inside, but can't seem to open the plastic casing without risking damaging it (it is in a new Fusebox CU yet to be installed).
 
It really depends on the SPD whether it needs an OCPD.
Its my understanding that SPDs are designed to fail open circuit. Pretty sure they are manufactured with a small soldered joint which is spring loaded, this is designed to melt under high fault currents and break the contact.
I’ve been told this by Robin from Dehn.
However Kirsty from surge protection devices says the opposite.
Both sit on the jpel/64 section D apparently.....
[automerge]1587898727[/automerge]
I was going to look inside one, to see exactly what is inside, but can't seem to open the plastic casing without risking damaging it (it is in a new Fusebox CU yet to be installed).
Do it anyway haha
 
Hi Ian,
Yes you are correct in saying their is no internal ocpd but they are rated at 125a which for most domestic installs with 60 and 80amp cutouts, the DNO fuse is acceptable for last resort OCPD with less than 250mm 6mm cable in total on the internal LNE SPD cables. For an extra £3 a 32amp mcb can be added to supply the SPD to give protection aswell ?
Fit loads of 6 way boards in terrace houses round here and to fit the 32a for the spd means going up to a 10 way board.....Havnt found an 8way fusebox yet??
 
If the SPD has a "fail flag" on display then almost certainly it has the spring loaded solder joint as a thermal disconnect mechanism inside. Also the MOV type (as normally used for type 2 and some type 1 SPD) tend to fail open, perhaps spectacularly so if they get a big direct hit but you probably have other concerns at that point...

I'm sure somewhere on YouTube I have seen a video with one of them taken apart that shows this but don't remember who did it.
 
Fit loads of 6 way boards in terrace houses round here and to fit the 32a for the spd means going up to a 10 way board.....Havnt found an 8way fusebox yet??
Fusebox did an 8 way and then made the same enclose metal cutouts wider and a larger din rail to accommodate 2 more ways without having to re manufacture all the enclosure ( so the old 8 way enclosure is the same size as the new 10 way) . 6 rcbo s / 1 mcb for SPD and 3 blanks allowing for future upgrades would do the job.
 
Fusebox did an 8 way and then made the same enclose metal cutouts wider and a larger din rail to accommodate 2 more ways without having to re manufacture all the enclosure ( so the old 8 way enclosure is the same size as the new 10 way) . 6 rcbo s / 1 mcb for SPD and 3 blanks allowing for future upgrades would do the job.
They would if they fitted in place of an old wylex board that you’ve taken out ?
 
Lewden and the rexel own brands offer Type A
BG offer type A rcds, possibly rcbos aswell. I often swap an ac rcd for a type a when fitting ev chargers in bg boards.
As mentioned already Fusebox supply type A's
Quick look on cef shows Proteus, MCG, M2 all doing type A
Rolec also do them, usually for there own ev or caravan hook ups.
Plenty of options out there and if you cant find one for your make of board then you can always route a circuit through a standalone module.
 
I was going to look inside one, to see exactly what is inside, but can't seem to open the plastic casing without risking damaging it (it is in a new Fusebox CU yet to be installed).

Well I now have a failed Fusebox SPD, so took a look inside. It failed due to mechanical damage, not electrical. The solder joint has broken, so the green flag springs back, revealing the red "failed" flag behind it.
Fusebox SPD.jpg
 
Well I now have a failed Fusebox SPD, so took a look inside. It failed due to mechanical damage, not electrical. The solder joint has broken, so the green flag springs back, revealing the red "failed" flag behind it.
Can you show us the other side (MOV part) as well?
 
The other side is completely encapsulated in some white solid (non-rubber) potting compound, so there is nothing to see.
 

Reply to Only 2 brands for domestic type A rcd/rcbo + type 2 spd in board?? in the Electrical Tools and Products area at ElectriciansForums.net

Electricians Tools | Electrical Tools and Products

Thanks for visiting ElectriciansForums.net, we hope you find the Electricians Tools you're looking for. It's free to sign up to and post a question yourself to find a tool or tool supplier either local to you, or online. Our community of electricians and electrical engineers will do their best to find the best tool supplier for you.

We also have a Tiling Tools advice from the worlds largest Tiling community. And then the Plumbers Forums with Plumbers Tools Advice.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock