frenchy

hi can someone help me i have to run tails to an outside meter cu 20 meters away i have a duct installed but can i run tails this far or shuold i run an armoured and would ukpn allow a switched fuse to be in there cabinet or could i get away with an double pole isolater thanks for your help
 
The most you'll get away with in a DNO cabinet is a small KMF style switchfuse.

Any bigger and they'll start complaining no end. Problem is, is that a KMF isn't suitable for SWA as you cannot gland & secure the cable correctly.

An additional cabinet of your own, adjacent to the DNO one would be best IMO.
 